How we can re-range the DP transmitter, range is -0.5 to 2.0bara. new range is -0.5 to 5 bar
Answers were Sorted based on User's Feedback
Something is wrong with the stated situation. The stated range is in -0.5 to 2.0 bara, where bar is bar absolute.
An absolute pressure references absolute zero (a hard vacuum).
No measurement can be made below zero bar absolute because it violates the laws of physics.
While a DP transmitter can not make a negative absolute measurement, it can make a negative differential measurement where the low side pressure is higher than the high side pressure.
The method of changing the differential range depends on the brand/model of the transmitter.
- zero and span adjusting pots
- zero and span push buttons
- local indicator/push buttons
- HART communicator/modem-software
The first two require an applied reference pressure for zero and span.
The 3rd and 4th options might have a choice of applied pressure or entering values for zero and span.
Some DP transmitters do not have the same accuracy in the negative range as they do in the positive range.
Carl Ellis
Measure First
| Is This Answer Correct ? | 4 Yes | 1 No |
What is the procedure of calibration of Load cell?
While giving Power Supply of 24 VDC to a Transmitter,why Shield Terminal is connected either at Transmitter or at ISB.Why not Shield Terminal connected at both ends.If the Reason is to avoid Noise interference,which type of noice that is interfering.Is the Noice from the 24 VDC supply terminals or from any external source.
1. How many output signals do wew have in process control? 2. Could you write down the names of the pre-commissioning and commissioning stage test instruments and explain them (more than 5 items)? 3. What is the first step to commission a transmitter on service? 4. What is RTD? 5. Find the output value in MA of a temperature transmitter (RTD Type) at 120degree celius? 6. What is the O/P signal of a pneumatic transmitter? 7. What is the O/P signal of an elctronic transmitter? 8. What is the close loop and open loon?
what is the principale of vortex flow meter.
7 Answers Ambuja, India Glycols,
what is piezoelectric transducer?give an example in power plant n state its principle?
Speedtronic system .
need to calculate flow rate with the help of dp range and orifice bore dia and size. range is 0 to 400 inwc and orifice size is 12 inch 150 # rf and bore dia is 7.180 inch. need to calculation for flow rate
I want to know if flowrate increases in 16' pipe line what will happen to upstream pressure and why?
How to consider the flow directions for control valve (Globe) Is the there any easy understanding in order to select the flow directions?
what is the name of thermocople element cable from field to pannel end?
what is difference between 1/2"NPT & M20 x 1.5 cable gland?
how to relay switch sense the fault?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)