How much current can 11KV line carry? What are the
formulae used to calculate current across both side of
transformer? Moreover I need to know can I connect 33KV
line with transformer of 1600KVA? Details are: V=415,
Pf= .9
Answers were Sorted based on User's Feedback
Answer / arulkumaran
KW = KVA*PF
KW = 1600*0.9
KW = 1440
11KV PRIMARY CURRENT=
KW = 1.732*KV*I*PF root(3) = 1.732
1440 = 1.732*11*I*0.9
1440/1.732*11*0.9 = I
I = 83.98 AMPERE
415V SECONDRY CURRENT=
WATTS = 1.732*V*I*PF
1440000 = 1.732*415*I*0.9
I = 2226 AMPERE
| Is This Answer Correct ? | 80 Yes | 20 No |
Answer / manimaranmuthu.m
11KV PRIMARY CURRENT[HT]:
KW = KVA*PF
POWER [KW]= 1600*0.9
POWER = 1440 KW
POWER [KW]=√3*KV*I*PF
root(3) = 1.732
1440 = 1.732*11*I*0.9
1440/1.732*11*0.9 = I
I = 83.98 AMPERE
415V SECONDRY CURRENT[LT]:
WATTS = 1.732*V*I*PF
1440*1000 = 1.732*415*I*0.9
I = 2226 AMPERE
| Is This Answer Correct ? | 29 Yes | 13 No |
Primary side voltage be 11KV,
Transformer's capacity= 1000KVA
Real power= Apparent*Power factor
KW=KVA*Power factor
if Power factor = 0.95
Power= 1000*0.95
Power=950KW
We also know,
Power(KW)=(root 3)*(KV)*I*Power factor
950=1.732*11*0.95*I
I(Current)= 49.7A
Secondary Voltage Be 433V
We know that,
Power(watts)=(root 3)*V*I*Power factor
Power=950KW=950000W
950000=1.732*433*I*0.95
I= 1333.4 A
| Is This Answer Correct ? | 9 Yes | 7 No |
what happen if i change the polarity of ac when it is connected with motor
How halogen & merquery lamp works.
what about the power of wattmeter at starting and loding?
can we run AC & DC cables in same tray
Graphs of measuring power and speed on dc motor
Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?
What is difference between ON delay and OFF Delay Timer?
what is the function of governor in dg set
1 Answers Igarashi, Medispray, Reddy Labs,
can we correct the p.f.of ac generator?
what is the principle of generator , induction motor,d.c motor
why when i start my diesel generator it takes 1 minute or less then stop, and i checked the oil sensor is ok and when the generator start i can get 220 voltage but it it is stop after 1 minute or less, how can i solve this problem?
What is Working principle of electronic choke?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)