Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How much current can 11KV line carry? What are the
formulae used to calculate current across both side of
transformer? Moreover I need to know can I connect 33KV
line with transformer of 1600KVA? Details are: V=415,
Pf= .9

Answers were Sorted based on User's Feedback



How much current can 11KV line carry? What are the formulae used to calculate current across both ..

Answer / arulkumaran

KW = KVA*PF
KW = 1600*0.9
KW = 1440
11KV PRIMARY CURRENT=
KW = 1.732*KV*I*PF root(3) = 1.732
1440 = 1.732*11*I*0.9
1440/1.732*11*0.9 = I
I = 83.98 AMPERE
415V SECONDRY CURRENT=
WATTS = 1.732*V*I*PF
1440000 = 1.732*415*I*0.9
I = 2226 AMPERE

Is This Answer Correct ?    80 Yes 20 No

How much current can 11KV line carry? What are the formulae used to calculate current across both ..

Answer / manimaranmuthu.m

11KV PRIMARY CURRENT[HT]:


KW = KVA*PF


POWER [KW]= 1600*0.9

POWER = 1440 KW

POWER [KW]=&#8730;3*KV*I*PF
root(3) = 1.732

1440 = 1.732*11*I*0.9

1440/1.732*11*0.9 = I

I = 83.98 AMPERE

415V SECONDRY CURRENT[LT]:

WATTS = 1.732*V*I*PF

1440*1000 = 1.732*415*I*0.9

I = 2226 AMPERE

Is This Answer Correct ?    29 Yes 13 No

How much current can 11KV line carry? What are the formulae used to calculate current across both ..

Answer / suhailpro

Primary side voltage be 11KV,
Transformer's capacity= 1000KVA

Real power= Apparent*Power factor
KW=KVA*Power factor
if Power factor = 0.95
Power= 1000*0.95
Power=950KW
We also know,
Power(KW)=(root 3)*(KV)*I*Power factor
950=1.732*11*0.95*I
I(Current)= 49.7A

Secondary Voltage Be 433V
We know that,
Power(watts)=(root 3)*V*I*Power factor
Power=950KW=950000W
950000=1.732*433*I*0.95
I= 1333.4 A

Is This Answer Correct ?    9 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

what will happen if dc supply is given to ac motor?

9 Answers   CTS,


what is metering cum synchronizing panel and how it is used?

0 Answers   Wipro,


how to calculate the neautral earthing conductor size for a 500kva dg set.

2 Answers  


Why 1/3 is used in symmetrical components?

0 Answers   ABB,


which motor used in electric train ans how much volt.

4 Answers   Trimax,


is there any current and voltage drop on liquid resistance starter water/soda tank ?

0 Answers  


bit confused - am i correct in thinking that to determine line to line voltage in a star config 110v 3 phase 4 wire distribution system i would use a voltmeter? I have a circuit configured as an unbalanced load, consisting of three incandescent lamps (1x40w, 1x60w, 1x100w - all 110v rated)connected in a star configuration to a 110v 3 phase 4 wire distribution system. I want to find out what types of meters i would use to obtain: a) each line to line voltage b) the line to neutral voltage across each load c) current flowing in each line and load d) current flowing in the neutral conductor e) power supplied to the loads im assuming i would be using ammeters in series along each line and voltmeters in parallel across each line to neutral? Also how could i predict these meter readings before taking them and with which formulae? Any help would be greatly appreciated A.

1 Answers  


What are the disadvantages of thermal power plant?

0 Answers  


What can make the the overloads operate when a star delta three phase motor starts?

1 Answers  


11 kv line me tino phase takra jaye to present time me approximately voltage aur current kya hoga...

2 Answers   Electrical, Electrical Tech, Videocon,


how to find ratio of CT & PT in 66/11kv 12 mva supply system ? explain with calculation.

0 Answers   Adani, Mahaveer,


i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)