How to calculate kva? what is the formula.
Answers were Sorted based on User's Feedback
Answer / kumar.m
In single Phase- p=VxI/1000
In three phase - P=route3xVxIxcosphi/1000
Is This Answer Correct ? | 89 Yes | 26 No |
Answer / nick a.
square root of 3 (1.732) x E x I /1000 =kVA (3 ph )
E x I / 1000 = kVA
120 x 60 =720 /1000 = kva (single phase)
Is This Answer Correct ? | 31 Yes | 6 No |
Answer / prithvi narayan sinha
kw/kva=cos(phi)
therefore kVA=kW/cos(phi)
Is This Answer Correct ? | 21 Yes | 5 No |
Answer / aayush
For Single Phase-
P (KVA)= V (Volts) * I (Amps)/1000
For Three Phase-
P (KVA)= 1.732 * V (Volts) * I (Amps) * CosQ/
1000
Is This Answer Correct ? | 20 Yes | 7 No |
Answer / joban
p=VxI/1000 in singl phase
p=root3xVxIxCosphi/1000
Is This Answer Correct ? | 18 Yes | 7 No |
Answer / nani
some pepole are writing for power actually asking for how
to calculate KVA.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / arun reddy
Take 3phase Current for Example.
R-24, Y-29, B-27.
24+29+27=80amps
80X230 (output volt)
18400/1000=18.4KVA.
Is This Answer Correct ? | 33 Yes | 29 No |
How we can determine short circuiting current any plant and for example a plant which power generation is 415 volts and plant load is 500 kw.
what are the merits and demerits of synchronous motor over an induction motor...??
whenever a squirrel or a crow gets tangled near the out put of the feild transformer there is a discharge of 440 volts of current through the neutral due to which my appliances blow up causing a huge bang.will the RCCB help in these conditions
what is resticted earth fault protection ? how did it protect & work in power transformer
DEAR SIR, HOW TO CALCULATE WELDING TRANSFORMER CAPACITY IN KW OR KVA (POWER). TWO WELDING TRANSFORMER USED WHAT TYPE OF DG SET CAPACITY LIKE ( 45 KVA OR 62.5 KVA), PLEASE TELL THE WELDING TRANSFORMER RATEINGS. I AM REFINARY (TANKS WELDING) THANKING YOU
what is advantage in open delta connection?
how can you calculate the value of external resistance inserted in a slipring industion motor? (eg. 110 kw / 990 rpm/50Hz/stator v-415/stator Amp-195/Rotor V-440/Rotor amps- 151.)
power 148kw i need exat cable size in 148 kw in 3phase what size of cable can i used.
What is the acessaries distribution transformer ?
Why Ferranti effect is occoured in leading power factor load in a overhead transmission line?
What is the meaning, function and application of OLTC?
The capacity of the transformer is 20/25 MVA, Ratio is 132/11 KV, Vactor group YNyno. and impedance is 10.07%. As per the calculation the secondary current is 1312.2Amps. The maximum fault current the transformer should sustain is 13.030KA. How many times the transformer should sustain the maximum short circuit current of 13.030KA over a period up 1 Year. The transformer is repaired one & 10 Years old.