Answer / jaswinder
% impedence is use to determine the max fault current the
transformer is capable of delivering to a downstream short
circuit.
Fault current=FLC*100/%imp.
this fault current is use to cal fault MVA
Fault MVA = 1.732 x fault current x V.
eg: If transformer of 2000kVA,5%imp having flc of around
1200A is use to supply to a motor of same flc carrying
capacity and if the voltage drop at transformer terminal is
more than the permissible voltage drop (+- 10%)during
stating of motor then the above transformer will be of
lower rating hence we have to select the transformer rating
higher than 2000kVA eg:-3000kVA (In other words transformer
having higher SC current capability ).If voltage remain
within the rated voltage of the motor then no oversizing of
tranformer is required.
Is This Answer Correct ? | 8 Yes | 1 No |
what is the difference between diode and zener diode?
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
what is the pressure of vacuum circuit breaker
Why sometime i receive GCU fault /Excitation voltage loss in my Generator Synch Panel .
can v rotate single phase induction motor in both the direction...?
In the magnetic fluxes, what is the role of armature reaction?
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
Does the direction of rotation of d.c. Shunt motor would get reversed if the armature current and field current both are reversed?
what is meant by LT & HT?
In a Circuit how the MCB and Fuse ratings are calculated. And shall the fuse follws the MCB or it is otherwise?
16 Answers Emerson, HCL, Thirumalai Chemicals,
The rating of Transformer are 11KV, 22KV, 33KV instead of 10KV, 20KV & 30KV?
What is cross over distortion? How it can be eliminated?