If the maximum demand is 120 KVA in a building, then what is
the Current taken according to load given ? Formula for it ?
Answers were Sorted based on User's Feedback
Answer / jose
120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr
Is This Answer Correct ? | 6 Yes | 0 No |
a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120
Is This Answer Correct ? | 2 Yes | 1 No |
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?
lamination figures
How will you Protect aeroplanes and Ships from Lightining?
What is meant by H.R.C fuse?
40 Answers Gas Projects, GSCE, Taj Group,
Relay setting for earth fault of reciprocating and centrifugal compressor motor feeder.Setting will be different or same?
what is the use of ballast in tube
On 400 amp factory load how kvarh capacitors provide
What is the typical power circuit configuration of a VVVF Drive ?
How to convert KVA rating into HP rating?
A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?
how much rating of fuse and MCB should be used for a load consisting of 6KW and 18KW inductive load?
To determine the Healthiness of Insulation we will be performing Dielectric tests i.e Insulation Resistance test, Partial Discharge test,Switching Impulse, Lightning impulse, Tan Delta test ...etc why we required to perform this many test, why cant we do only one test. for Transformer, CT's