If the maximum demand is 120 KVA in a building, then what is
the Current taken according to load given ? Formula for it ?
Answers were Sorted based on User's Feedback
Answer / jose
120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr
| Is This Answer Correct ? | 6 Yes | 0 No |
a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120
| Is This Answer Correct ? | 2 Yes | 1 No |
Which element is highly conducting coppoer or gold?
How to know motor winding is star or delta connected without see the information table and winding connection ?
How to test IR testing & magnetic balance test
If oil and air can withstand a high MeV when used as an insulator in a transformer, what are the values of how high for each material?
how to read idmt curva
explain about the electrification in the Indian Railways? ie., how the power is taken and used to drive the train? explain with the block diagram??
Why not LED burn after showing alarm,as Alarm volt is 11- 13,But LED is of3 volt,why it isnt Burn??
why write 500v on line tester (Test pen)
What is pi controller?
Which is the largest hydropower station in the world?
what is the working principle of induction motor
How voltage regulation is calculated for over head transmission line? What do we mean by Conductor constant while calculating voltage regulation? how it is differ for for diffrent type of conductor say AAAC DOG & AAAC RACOON conductor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)