If the maximum demand is 120 KVA in a building, then what is
the Current taken according to load given ? Formula for it ?

Answers were Sorted based on User's Feedback



If the maximum demand is 120 KVA in a building, then what is the Current taken according to load gi..

Answer / jose

120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr

Is This Answer Correct ?    6 Yes 0 No

If the maximum demand is 120 KVA in a building, then what is the Current taken according to load gi..

Answer / basharat khan

a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120

Is This Answer Correct ?    2 Yes 1 No

If the maximum demand is 120 KVA in a building, then what is the Current taken according to load gi..

Answer / rajamanickam

KVA=V*I; KW=KVA*COS

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What are the minimum acceptable insulation resistances of insulation of underground cable suitable for 0.440kV,11kV, 33kV and 66kV?

2 Answers  


Compare jfet’s and mosfet’s.

0 Answers  


What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?

2 Answers  


What is the types of HT motor testing

0 Answers   ABB,


How I design capacitor bank for different load.7MW connected load.

3 Answers   Samtel,






what is the primary current in 415/415 v when secondry of dry type transformer is shorted.?

3 Answers  


During speed control of dc shunt motor with flux control methode,when armature voltage is constant, How can it possible to increasing the armature current?

1 Answers  


What is AVR in Generators and How is it working.

4 Answers  


We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).

3 Answers  


What is the Ohms low calculation

2 Answers  


how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?

0 Answers  


Transformer Specification say 66/11KV, 23/27/35MVA OFDAN,what is OFDAN? we know ONAN,ONAF or OFAF

2 Answers   Siemens,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)