If the maximum demand is 120 KVA in a building, then what is
the Current taken according to load given ? Formula for it ?
Answers were Sorted based on User's Feedback
Answer / jose
120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr
Is This Answer Correct ? | 6 Yes | 0 No |
a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120
Is This Answer Correct ? | 2 Yes | 1 No |
What are the minimum acceptable insulation resistances of insulation of underground cable suitable for 0.440kV,11kV, 33kV and 66kV?
Compare jfet’s and mosfet’s.
What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?
What is the types of HT motor testing
How I design capacitor bank for different load.7MW connected load.
what is the primary current in 415/415 v when secondry of dry type transformer is shorted.?
During speed control of dc shunt motor with flux control methode,when armature voltage is constant, How can it possible to increasing the armature current?
What is AVR in Generators and How is it working.
We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).
What is the Ohms low calculation
how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?
Transformer Specification say 66/11KV, 23/27/35MVA OFDAN,what is OFDAN? we know ONAN,ONAF or OFAF