If the maximum demand is 120 KVA in a building, then what is
the Current taken according to load given ? Formula for it ?

Answers were Sorted based on User's Feedback



If the maximum demand is 120 KVA in a building, then what is the Current taken according to load gi..

Answer / jose

120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr

Is This Answer Correct ?    6 Yes 0 No

If the maximum demand is 120 KVA in a building, then what is the Current taken according to load gi..

Answer / basharat khan

a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120

Is This Answer Correct ?    2 Yes 1 No

If the maximum demand is 120 KVA in a building, then what is the Current taken according to load gi..

Answer / rajamanickam

KVA=V*I; KW=KVA*COS

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?

3 Answers  


lamination figures

0 Answers  


How will you Protect aeroplanes and Ships from Lightining?

3 Answers   Parco,


What is meant by H.R.C fuse?

40 Answers   Gas Projects, GSCE, Taj Group,


Relay setting for earth fault of reciprocating and centrifugal compressor motor feeder.Setting will be different or same?

1 Answers   Reliance,






what is the use of ballast in tube

2 Answers  


On 400 amp factory load how kvarh capacitors provide

0 Answers  


What is the typical power circuit configuration of a VVVF Drive ?

1 Answers  


How to convert KVA rating into HP rating?

6 Answers   AITM,


A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?

0 Answers   L&T,


how much rating of fuse and MCB should be used for a load consisting of 6KW and 18KW inductive load?

1 Answers  


To determine the Healthiness of Insulation we will be performing Dielectric tests i.e Insulation Resistance test, Partial Discharge test,Switching Impulse, Lightning impulse, Tan Delta test ...etc why we required to perform this many test, why cant we do only one test. for Transformer, CT's

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)