How I design capacitor bank for different load.7MW
connected load.
Answers were Sorted based on User's Feedback
the capacitor bank depends on the load type
1. for resistive load no need cap.bank
2.and the cap.bank calculation depends on the Power factor
(for inductive loads 0.8 pf lag)
if u want clear calculation mail me with all load perticulars
mail id: viswaeee60@gmail.com
Is This Answer Correct ? | 3 Yes | 4 No |
the capacitor bank reqired almost 30 persent of full load
(kva) but exectly we must know the desired powerr factor
KVAR = kw/Sin theta
pf= cos theta= desired pf
let 0.99 we require than cos Q = 0.96
Q= Cos inv 0.96
SinQ Will = sin * Q
Kvar = Sin Q* Load
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / mior
First and foremost, you need to know what is your required
KVAr; then, you can design the capacitor bank to suit with
your required KVAr.
The purpose of designing the capacitor bank is to correct
the power factor to the desired value. By doing so, you can
reduce the loses of power as well as reducing your
electricity bill.
The link below might help you on how to design the power
factor correction and how to design the capacitor bank.
http://guide4electricalconsultant.com/power%20factor%
20correction.html
http://guide4electricalconsultant.com/design%20cap%
20bank.html
Is This Answer Correct ? | 1 Yes | 5 No |
How does a VOLTAGE OPERATED DIFFERENTIAL RELAY work??
why does the magnetic balance tests at transformer?
why we use star connection in HT motor? and delta connection in LT motor
We have one 500KVA transformer. We have tested REF relay and commissioned. After one and half year, due to some ground fault in one of the DB circuit Transformer tripped by REF relay. What will be cause and remedy. Please advise?
Sate maximum power transfer theorem?
What is the d/f between DOL & star delta starter & automatic star delta starter?
23 Answers ACC, Dalkia, Engineering, Indeco, NINL, Novotel, RMH Control Systems, Wipro,
Write down the name of 2 lady Bir Pratin of Bangladesh
Relation between Sq.mm of wire and Its current carrying capacity?
What is an alternator impedance value?
The synchronous machine excitation system explain
what is differents between static stablizer and servo stablizer
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..