What kinds of decision are made about CT from it's Knee
point(voltage & current)?
Answers were Sorted based on User's Feedback
Answer / shariff
Knee Point Vog is the Point where the Votlatge shouts up
and the Current gets saturated for the CT across its cors
and it is a very vital parameter for any current
transformer. And this Knee Voltage value should be same for
all the 3 phases of the CT.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / raj
For Protection CTs knee point voltage is always high than
Metering CTs to avoid saturation of CTs during fault
current.But to increase the knee voltage core size should
be increase which is practically possible or economical so
another method to reduce the burden on CTs by using
secondary ratio 1A inplace of 5A.
Is This Answer Correct ? | 1 Yes | 0 No |
its Kva and Kv are same?
What is the Levels of High Voltage, Medium Voltage & Low Voltage?
What is 100% protection of generator? Why 100% is not used but 95% is generally used?
How many capacitors using in LT panel as per Govt rules?
advantages & Disadvantages of Solar power system?
Disadvantage of leading power factor
what is meant by phase transformation ratio in induction motors?
What is the make of breakers, transformers, generators? What are their capacities and ratings?
what is meant by the phrase 'static load' in case of shorting in a generator excitation system?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
How to calculate MCB Breaking capacity.
How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size of cable is used for this motor.