How you calculating the current for a 2.5 Sqmm cable.
A 30 Hp 3 phase AC motor of power what size of cable is
used for this motor.
Answers were Sorted based on User's Feedback
the answer is wrong we can calculate by usbing this formula
W = 1.732*V * I Cos (phi)
30*746 = 415 * I * 0.8*1.732
I=36.2 AMP
| Is This Answer Correct ? | 24 Yes | 6 No |
Answer / shashank
deciding a cable has to consider following parameters also,
1. Safety factor of the cable (margin for starting current
say 1.25 in numerator side)
2. Deterioration / Degradation factor (say 0.8 in
denominator)
calculate the current of the motor by considering running
pf (power factor) say 0.8
as motor gives real power
e.g.
W = V * I Cos (phi)
30*746 = 415 * I * 0.8
I = 30 * 746 / (415*0.8)
I = 67.41 Amp,
Thus Current considered for cable (Icb) = 67.41*1.25/0.8
Icb = 105.3 Amps.
Select from the catalogue suitable copper cable for this
motor. Dont forget to consider the voltage drop per meter,
the total voltage drop shall not be more that + - 5%.
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / balakrishnan.t
For calculating the current rating of a 30 Hp 3 phase motor can be written as
power = sq root(3)* VL*IL*cos (phi)--------(1)
where 'VL' is line voltage, 'IL' - line current and cos phi- power factor
OR 3 EP*IP*cos(phi)
as the voltage fed is from three phase system.
Power input of 30 Hp motor = 30*746/(efiiciency*cos phi) watts
from the formula (1) and taking efficiency as 0.9,
Line current 'IL' = 30*746/(1.732*415*0.9*0.83)
= 41.68 Amps
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / ramesh insan
As per thumb rule
Power Sq root 3=1.732
Voltage =415
PF=0.8
Cos=0.85
1.732*415*0.8*0.85=488.77
30HP*746W=22380/488.77=45.79 Amp
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amarnath
If its a 2.5Sq.mm Aluminium cable then it can take load
current upto 3Amps and if its Copper cable then it can take
a load current upto 9.4Amps.
And for a 30HP motor the cable size shall be 3.5Core X
16sq.mm Aluminium or 3.5Core X 6sq.mm Copper cable.
| Is This Answer Correct ? | 17 Yes | 23 No |
how many earthing should need for UPS, where its connected
what are the main parts of DG? explian thier functions?
8 Answers Apollo Power, Tata DoCoMo, Tyco, Vizag Steel,
what is post close & pre close of trip circuit supervision relay in circuit breaker control scheme?
difference bteween neutral grounding resistor and neutral grounding transformer??
How many no. of earthing pits required for commisioning a new 320KVC DG Set????How????
can I improve the furnace power factor (10 mva transformer) by adding a capacitor bank before the transformer.Does system power factor vary a lot with the furnace PF?
what are inductive and capacitive voltage transformers.what are their applications
What is the working principle of ceiling fan?
What is the meaning of ST and HT in electrical transmission and what are thier range.
WHAT IS THE DIFFERENCE BETWEEN VOLTage and potential diff
There is 15 KVA UPS using for single phase load.And 30 batteries of 12 V, 100 Ah are connected in series. Load is taking 15 A current.What will be the back up power for this UPS on same load?
1 Answers BS, Dynamic Software,
What is the basic difference between AVR and stabilizer?
2 Answers Gujarat Alkalies and Chemicals GACL,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)