Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How you calculating the current for a 2.5 Sqmm cable.
A 30 Hp 3 phase AC motor of power what size of cable is
used for this motor.


Answers were Sorted based on User's Feedback



How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shoyabkhan

the answer is wrong we can calculate by usbing this formula
W = 1.732*V * I Cos (phi)
30*746 = 415 * I * 0.8*1.732
I=36.2 AMP

Is This Answer Correct ?    24 Yes 6 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shashank

deciding a cable has to consider following parameters also,
1. Safety factor of the cable (margin for starting current
say 1.25 in numerator side)
2. Deterioration / Degradation factor (say 0.8 in
denominator)
calculate the current of the motor by considering running
pf (power factor) say 0.8
as motor gives real power
e.g.
W = V * I Cos (phi)
30*746 = 415 * I * 0.8
I = 30 * 746 / (415*0.8)
I = 67.41 Amp,
Thus Current considered for cable (Icb) = 67.41*1.25/0.8
Icb = 105.3 Amps.
Select from the catalogue suitable copper cable for this
motor. Dont forget to consider the voltage drop per meter,
the total voltage drop shall not be more that + - 5%.

Is This Answer Correct ?    15 Yes 9 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / balakrishnan.t

For calculating the current rating of a 30 Hp 3 phase motor can be written as
power = sq root(3)* VL*IL*cos (phi)--------(1)
where 'VL' is line voltage, 'IL' - line current and cos phi- power factor

OR 3 EP*IP*cos(phi)
as the voltage fed is from three phase system.
Power input of 30 Hp motor = 30*746/(efiiciency*cos phi) watts
from the formula (1) and taking efficiency as 0.9,
Line current 'IL' = 30*746/(1.732*415*0.9*0.83)
= 41.68 Amps

Is This Answer Correct ?    6 Yes 3 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shamsher singh

10sqmm cooper

Is This Answer Correct ?    1 Yes 1 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / ramesh insan

As per thumb rule
Power Sq root 3=1.732
Voltage =415
PF=0.8
Cos=0.85

1.732*415*0.8*0.85=488.77

30HP*746W=22380/488.77=45.79 Amp

Is This Answer Correct ?    0 Yes 0 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / amarnath

If its a 2.5Sq.mm Aluminium cable then it can take load
current upto 3Amps and if its Copper cable then it can take
a load current upto 9.4Amps.

And for a 30HP motor the cable size shall be 3.5Core X
16sq.mm Aluminium or 3.5Core X 6sq.mm Copper cable.

Is This Answer Correct ?    17 Yes 23 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / mrudang

we are measure through SWG ( standard wire guage
it measure the crossection of wire
2.5sqmm

Is This Answer Correct ?    13 Yes 20 No

Post New Answer

More Electrical Engineering Interview Questions

What is the direction of current flow in ct secondary...means if the current is flowing from P1 to P2 then what will be the direction of current flow in ct secondaryw

0 Answers  


what is difference between 3.5 core and 4 core cable

5 Answers   Havells,


What is the effect of using an underrated size cable to supply electrical power to a 3 phase ac electrical motor? What is the effect of using an overrated size cable for the same motor?

1 Answers  


why do the alternator doesnt have open circuited windings in armature???

1 Answers  


1)What will happen when 240 VDC supply is connected to 240VAC supply(DC supply +ve is connected to phase of AC supply & DC supply is to neutral of AC supply). 2)Also what will happen when 240 VDC supply is connected to 240 VAC supply in reverse polarity as of Sr. No 1.

2 Answers  


3 phase induction motor rotor field rotate at synchronous speed w.r.t ?

3 Answers  


What are the advantages of using distance protection schemes as opposed to normal overcurrent/ earth fault protection on high voltage feeders.

0 Answers   Eskom,


wap to print prime number from 1 to 100 using c++

1 Answers  


what is second harmonic, how is effect transformer ?.

2 Answers   DEWA,


What is the purpose of Vector Group in transformer?

1 Answers   Andritz, ThyssenKrupp,


Brief use of isolation transformer & how it works.

1 Answers  


As per standard, transformer body earthing and other Equipment earthing (Equipment earthing) did not connect. but in LT side termination we are doing metal glanding in both side Transformer to PCC Panel through armoured cable, now X'mer body earthing and PCC Pane earthing (Equipment earthing) both are connect.is this safe for X'mer or other equipment?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)