Answer / maranatha
in t/f core and cu losses are occur these losses are
depending on voltage and current and it is independent of
power factor so t/f rating kva
| Is This Answer Correct ? | 15 Yes | 4 No |
IN ANY MACHINE THE RATING DEPEND UPON HEAT,HEAT LOSS DEPEND
ON HOW MUCH OF POWER LOSS IN THE MACHINE,IN THE TRANSFORMER
THE CORE LOSS DEPENDS ON VOLTAGE AND COPPER LOSS DEPENDS ON
LOAD CURRNT,i.e NO LOSSES DEPEND UPON POWER FACTOR THAT IS
THE TRANSFORMERS ARE RATED IN KVA INSTEAD OF KW.(reffer in
p.s bimbra text book electrical machines)
(OR OTHER WORDS)
KW RATTING IS DEPENDS ON POWER FACTOR ,THAT IS KW VARIES
WITH LOAD POWER FACTORS ,IF TRANSFORMERS RATED KW THE
RATING CHANGE WITH LOAD TO LOAD ,THAT IS THE TRANSFORMERS
ARE RATED IN KVA INSTEAD OF KW.(GENERAL ANSWER
rajeee43@gmail.com)
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kotaprolu.raneela
fffffff
in transformer we only bother with voltage rating and
losses.the 3 phase power is given by [sqrroot3* vi cos
(fi)].the power factor cos(fi) depends on the load we
connect.we dont know the type of load.so the rating of
transformer is in kva but not in kw...
| Is This Answer Correct ? | 4 Yes | 2 No |
As we know,capacity of conductor carrying conductor is
fixed in a perticular atmospheric conditions.Current in
transformer or DG set or alternators depends on load power
factor, current drawn by a perticular KW machine is more if
power factor is low whereas same KW rating machine wil draw
less current if it has high power factor.Hence
Transformer/DG/Alternator can not be designed for KW but
for KVA rating.It will feed high KW with high power factor
and low KW with low power factor without damaging winding
conductor/insulatin.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / deepankar
In fact,
generally there is no
neutral or return
conductor on the
primary side of
transformer and hence
all reactive power
demanded by load is
fed by transformer
itself. In this sense
transformer power is
independent from
powerfactor. That is
why transformer rating
is in kva.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sakthivel
if any electrical apparatus rating are depend on power
factor, transformer rating (are permanent load we not fixed
or base load are we not fixed so we noted the rating of
transformer rating )is KVA vanthni@yahoo.com
| Is This Answer Correct ? | 2 Yes | 2 No |
WHAT IS DIFFERENCE BETWEEN PHASE CONVERTER AND VFD
why transmission voltage is 230kv and not 220kv which is a multiple of 11
1 Answers Mettur Thermal Power Station, Siemens,
what is the difference between a hooter and a mcp
If two Transformers are connected in parallel having impedance of 50KA in both transformers will the impedance increase or decrease after connecting transformers in parallel?
For 6600/433 distribution transformer we apply secondary side 433 volts how much voltage in primary side.
What is load staggering or load shifting in the context of power distribution?
what is standard height of an energy meter from ground?
what are check points to be checked while charging switchyard?(CT,PT,BREAKER,POWER TRANSFORMER)
can you show me the components inside a air circuit breaker with connection diagram?
what is the criteria for selecting fuse rating in 1phase, 2phase & 3phase welding sets?
what is back trip and re-trip in protection schemes? why these two? define me the exact function of these two?
what is 30-phase of transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)