Answer / nitin bhoraokar , power plant
In delta - delta type winding connections,protection against
earth fault is difficult as zero sequence current will get
circulating in windings itself & will not flow to ground.
Hence transformer isolation on earth fault is
hectic.Stability against E/F will get lost.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / abc
Generally Transformer at generating station and at load
centres can not be used in delta-delta fashion due to non
availability of neutral point.
But if load is delta connected or in case of transmission
lines at both side then delta delta fashion can be used.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / subaharan
delta-delta transformers are using in high power required areas.power transmitting areas transformers,transformers parallel connection areas these type of transformers are used.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suhail a.
Because generally in transformers we need to get a neutral
point form the star that is what we r not using the delta to
delta.
| Is This Answer Correct ? | 2 Yes | 3 No |
what is maximum or Threshold value of current 7 voltage that a common man can withstand
what about electrical pannel.? What is meant by plc pannel.?
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
we have 15 ampere variyac but we want 30 ampere variyac what we do
RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED FOR OVER VOLTAGE PROTECTION SO WHY NOT THE RATING OF LIGHTENING ARRESTER BE MORE THAN 11KV ???????????????//
Define cut-off rate?
How to create a SCADA diagram on PC? I run the DG everyday but i dont know how that animated single line diagram is created.Please answer.
what is the difference between LT & HT Motors
distribution transformer de-rating formula on over limit iron losses
Define de-sensitivity?
What is neutral earth voltage of transformer and what should be the value
The power showed in the name plate of the motor is input power or output power?? The power showed in the name plate is 18.5kw measured current is 34.5 amps. location is india. can i calculate the efficiency of the motor using this data??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)