?? how to calculate lighting system ????
Answer / soumya
N=E*A/(F*U.F*L.L.F); N= number of light fittings required;
E = Lux required in working plane
A = Area of the room
F = Total Flux (Lumens) from all the Lamps in one Fitting
UF = Utilisation Factor = 0.46 (approx)
LLF = Light Loss Factor OR maintenance factor = 0.8 (approx)
Is This Answer Correct ? | 0 Yes | 0 No |
when qty of cable being purchased is not sufficient according to the standard,what should the inspector do to ensure its quality according to the standard?
Why capacitor bank does not require in DG Set?
what is the impedence
In case of 11kV dual delta bank what are the recommended protections with specific CT / VT requirements? The capacitor bank is to be connected to the main 11kV switchgear from where the H.V.Motors and auxiliary 440V loads.
How many types of electrical earthing are there?
How can we get electric power from lighting ?
Difference between ELCB and RCCB?
What is CRT (Contact Resistance Test) for Isolators or Dis- connector Switches? Why we performed it & whats the Testing procedure.
What is Minimum permicible meggering value for following 1) LT Panels (Ph to Ph / Ph to Earth) 2) 11 KV, HT Panels (Ph to Ph / Ph to Earth) 3) 11 KV Cable 4) LT Cable
What is difference between 220v/50Hz & 120V/60Hz?
How can we calculate the KVA rating of a Distribution transformer from its core details?
what is the reactance,capacitance & impedence electrical armoured & unarmored Cables.