Hot Water System (HWS). Will a 30ma elcb have more nuisance
tripping than 100ma elcb
Answer / daniel tan
The nuisance tripping either for 30mA or 100mA is not so
crucial when Hot water system is concern. With reference to
IEC60479, the RCD/ELCB 30mA or 100mA is not safe to be used
for the Hot water system where it could result to a shock
hazard. As declared by this Standard, a normal human body
can only withstand to a maximum of <7mA. The Residual
Current Device (RCD) leakage protection ranges between
2.5mA~5mA/<50mS should be the correct level of protection
for any Hot water system or Instant water heater appliances
at Home. To prevent any shock hazard, look for RCD can
perform 2.5mA~5mA/<50mS. Let me know if you need help.
Is This Answer Correct ? | 1 Yes | 0 No |
how to calculate the speed of a induction motor without using tacho meter?
How much resistance between neutral earthing and body earthing of Power transformer?
what is conductor copnstant of ab cable
WHAT IS DIFFERENCE BETWEEN PHASE CONVERTER AND VFD
what happens if number of poles in stator and rotor windins of slip ring induction motor are not same. Will it rotate near to the synchronus speed defined by stator?
why transformer donot allow the dc?
In a d.c current, the power is the product of voltage and current. This relationship does not always apply to effective(r.m.s) values in an a.c circuit. Explain the reason for this.
how to calculate the MF in meter reading
why we use separate earthing for two seprate machine??
Wat is da difference b/w neutral earthing and unearthed system?
Can anybody tell me why inductors draw lagging current and capacitors draw leading current from supply?
why the value of impedence is taken as %impedence in fault currrent calculation