Hot Water System (HWS). Will a 30ma elcb have more nuisance
tripping than 100ma elcb
Answer / daniel tan
The nuisance tripping either for 30mA or 100mA is not so
crucial when Hot water system is concern. With reference to
IEC60479, the RCD/ELCB 30mA or 100mA is not safe to be used
for the Hot water system where it could result to a shock
hazard. As declared by this Standard, a normal human body
can only withstand to a maximum of <7mA. The Residual
Current Device (RCD) leakage protection ranges between
2.5mA~5mA/<50mS should be the correct level of protection
for any Hot water system or Instant water heater appliances
at Home. To prevent any shock hazard, look for RCD can
perform 2.5mA~5mA/<50mS. Let me know if you need help.
Is This Answer Correct ? | 1 Yes | 0 No |
why hv winding is not placed near to transformer core
How can we calculate the resistance of earthing & how can we control it?
what are the advantages of Horizontal isolation breakers v/s vertical isolation breakers in medium voltage switchgear class.
How can get C license i am complete I.T.I electrician trade and 10 years experiance this field and i complete the dee from ksou by distance mode of this year.ksou means karnataka south open university but i want Tnelb license
What is the basic principle of operation of alternators/dc generators?
How much amperes needed for starting of 4HP motor?
what is the purpose of high speed earth switch in gas insulated substat
If we have two nodes A and B and Vab is the potential difference between these nodes then which node is called reference node a.node A b.node B c. Ground node
why it is mentioned as 8/10 mva transformer why not directly 8mva or 10mva transformer. please explain me the full detailed reason.
why does same amount of current flow in the circuit inspite of any number of resistances in the circuit?
how can u do the earthing of an aeroplane?
IF avr is voltage regulator of genset means why we are giving genset CT sense to AVR ?