why 4 to 20 ma? why cant some other range?
Answers were Sorted based on User's Feedback
Answer / g pravin
at 4-20ma with +24V power supply, no spark will be
generated.& 1 VDC at 4 mA of loop current and 5 VDC at 20
mA of loop current as per standard of analog i/o cards.
if we use 0 to 20ma instead of 4 to 20 ma then we can not
find actual position zero reference output, for example if
we have a motorized valve, it's full close at that time we
get 0ma (0%) reference and at fully open position we get
20ma (100%) reference, in this condition if power supply of
is off then we also get 0ma reference, so here in this kind
of
Condition we can't get actual result like that gate is
actually close or any other problems as per explanation of
above
Is This Answer Correct ? | 21 Yes | 4 No |
The 4 mA current has been selected for zero, so that we can distinguish the process zero condition from the supply failure condition. it is called the LIVE ZERO. If the process is zero then output will be 4 ma. If the instrument power is not available then it will give 0 ma. We can ensure the online availability of the instrument for measurement.
The noise pick up in the signal cables may be in the order of say 3.5 mA and so 4 mA has been fixed as zero. As a convention the span to zero ratio is fixed as 5, so that the span output signal comes to 20 mA. (3 to 15 psi, 1 to 5 Volts,0.2 to 1.0 bar etc.)
For remote signal transmission the cureent signal is preferred to voltage because of the drop in the signal cable. The supply voltage is 24 V will make up for the loss in case of current signal transmission.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / shijith c
only at 4-20ma output, we are getting linearity. Also, at 4-20ma with +24V power supply, no spark will be generated. for these reasons only 4-20 ma is selected.
Is This Answer Correct ? | 3 Yes | 8 No |
How do Foundation Fieldbus works? how the Communication Carries out from Foundation field bus,Field Devices and Controller? Were it's Application in the Field? For Which Signals this is Used? PLease Find this answer for this Question Detaile wise because i want to clear the Concept Regarding Foundation Field Bus,if Possible please attach the link of Document with Contails Diagramatic So that more esier for me.
can install leveltrol in steam drum for measurment the level of steam drum? if not then why?
plc trouble shootings?
How earthing can be checked????
what is actual difference between pressure Transducer & Pressure Transmitter.
for commissioning the DPT and Flow Transmitter , what kind of necessary activities we have to check and do? specially that orifice flange valve[ isolation valve}
what is the difference between two wire transmitter and 4- wire transmitter
what is cascade loop and how it work and why it used instead of PID single loop? In cascade, Which loop is faster and slower? Please explain with loop drawing and example...
What is the maximum operative of Drive ?
What is the principle of capacitance type level transmitter?
what is the current pay package for an instrumentation engineer having 2 years of experience in cryogenic technology???????
Dear All can any one told me that VFD Make ABB Model ACS800-01 used for dual Source like 1.DC Source applied at terminal UDC+,UDC- 2. 3 phase 400AC,50Hz