Answer / himanshu apte
As i understand the question, If 'D' value in PID is
changed, the process responds to the rate of change of
error between the PV & SP. In operation, controller first
compares current PV with the last PV value. If there is a
change in slope of PV, controller determines the output at
a future point in time. This future point in time
represents the derivative setting. Derivative mode
increases the output by that amount.
Advantage: Rapid o/p reduces time required to bring PV to
SP.
Disadvantage: Dramatically amplifies noise signals & can
cause cycling in fast process.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / swatihendre
If D increased then output response will be fast and if D
decreased then output response will slow
| Is This Answer Correct ? | 9 Yes | 1 No |
What should be the main consideration while starting the Rotating compressor when we dont know the cut in and the cut off pressure setting of the pressure switch
What is basic of instrumentation
What is the IEC Standard for PLC I/O Terminal wiring Procedure?
what is working principle of vibration prob
When can a bypass not used on a positioner?
We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
2 Answers National Petrochemical Company,
Is Hart communicator calibration device or communicating device for transmitter?
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
what is the PC interface and software for connection to ABB logic module “ LM011-CE18RAC “ ( for Programming ) ??
is any standard angle for thermowell mounting for horizontal and vertical pipe lines?
what is radar type level transmitters and its basic principle and how to calibrate it
what is the difference between -24 : +24 & 0:24 and where it use?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)