What is the formula to find out cross sectional area of
cable for certain current rating?
Answer / tarun aggarwal ymca
what u have to first take into mind what type of cable u want to purchase....then its size matter
usually we use XLPE insulated cable for Power cable and Aluminum or copper its depend upon the cost and loses
mean if u need large length cable you have to prefer aluminum in shorter length copper cable is preferred as its resistivity is less
for example
VLL = 11kV (line volatge)
L = 1.3km
Maximum allowable Vdrop = 2.5% of VLL i.e.Vdrop = 275V
SkVA = 3000kVA (Total Power we have to transfer of to be used by the connected load)
Full load Current If= SkVA/root3 VLL i.e If = 157.5A
Demand factor is what we actually demand the current (it not always full load current what we demand) Let D.F = 80% of If
Id =D.F x If (Demand Current) where D.F = Demand Factor i.e Id = 126.0A
The cable current carrying capacity is always kept larger than the demand current let S.F for Cable in % = 30% Extra Id
Ic= (1+S.F/100) Id i.e Ic = 163.8A
This current is what will be safer current that will be carried out by cable
Now derating factor K is calculated by the following equation
K = Kground x Ktherm.res x Kdepth x Kgroup
Vdrop = 3IdL root(Rac cos􀄳+ Xsin􀄳)
Now cable data is refered
Type 3 Core, Copper Conductor, XLPE insulated, Copper tape Screened, PVC bedded, Steel Wire Armoured, PVC, 8750/15000V.
Parameter -------- 50 mm2---- 70 mm2 ------ 95 mm2------- 120 mm2 ------- 150 mm2 ----- 185 mm2
Irated (A) --------- 187----------- 227- ------------ 267--------------303 -----------------338------------------ 383
Kground----------------0.86
Ktherm.res-- ----------- 1
Kdepth-------------------0.98
Kgroup ------------------0.7
K-------------------------- 0.590
Icor (A) -----------110.32 --------- 133.92----------157.52--------- 178.76-------------199.41------------225…
Rac (ohm/km) --- 0.493 --------0.342------------ 0.247------------0.196---------------0.1… ------------ 0.128
X (ohm/km) --------0.118 --------0.112 ------------0.106------------0.102------…
P.F = Cos--------0.85
(In radian)-------- 0.5548------ 0.5548----------0.5548-----------0.5548-…
Vdrop (V)-----------196.76-------167.73-------…
Considering the values of Ic, Icorrected and Vdrop the best suited cable is 120 mm2
cable for connecting switchyard to substation
Sorry extra long answer but i want to explain in detail
| Is This Answer Correct ? | 7 Yes | 2 No |
can we use ac ameter as dc ameter with ct
Why the stator is rotated in ceiling fans not Rator?
How to calculate no of Lighning arrestors are required for protecting 50mX 50m*20m cubical building and locations of LA?
WHY CURRENT DECREASES WHEN VOLTAGE IS INCREASED IN A CURRENT TRANSFORMER ?
What do u understand voltage reg. of an alternator?
if we convert kw into kva,which one formula use by us,pls tell me?
19 Answers ABB, AEC, BGH,
what type of protection and safety req. in the 220kv substaion and area around the substation
CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND TAKING OUTPUT FROM PRIMARY?
which Machine u will prefer to use at place where Flammable gases are coming out & why ??
How to calculate VA rating for CT or PT or Control Transformer?
How to identify the start and end of 3phase 12 lead motor if U1, U2, etc numberings are lost or erased.
what are the changes made in induction motor so that it act as induction generator
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)