A 3-phase IM is supplied from 50 Hz system. It runs at speed
of 1440 rpm and slip equal to 4 %. Calculate rotor
frequency.
A 50 Hz B 0 Hz
C 4 Hz D 6 Hz
Answers were Sorted based on User's Feedback
Answer / varaprasad
ANS: 2Hz
Rotorfrequency = s×frequency of applied voltage to stator = sf
SO,
ROTOR F = 0.04*50=2Hz
| Is This Answer Correct ? | 7 Yes | 0 No |
why don't we use the generator as a motor? and what will happen?
How to calculate the current carrying capacity of electrical cables
16 Answers Barqaab, Grasim, Havells, HM Cables, Janapriya, Polycab,
difference between Ac and Dc mcb ????
1]how the voltages and frequency are achieved on ships. 2]how does the line and phase voltages are related on ships.
if we know Fault level say 25 KA , How to decide busbar size for Distribution network of 1000 Amp Breaker ? Sample Calculation or Farmula Available or not ?
How to calculate the time setting for star connection in star delta starter? For example 10KW 3PH Induction motor.
0 Answers Taj Group, Tata Steel Limited,
Why DC exitation to AC Generator? Why not AC?
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
what is the current carrying capacity of 725 va generator
Can we loop AC neutral wire with DC neutral wire?
how induction motor starts?
hello if any one have papers vof hpcl or sail, plz send me
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)