what is exat meaning of compentation in RTD ? what diffrent
between 2 wire,2 wire and 4 wire RTDs?
Answers were Sorted based on User's Feedback
In RTD, we are measuring temperature through Resistance
change. Normally we are measuring this parameter in the
field. while transmitting, these signal to control panel
through cable, some additional resistance due to distance
will add upto the RTD resistance value. which shows
incorrect value. in order to overcome these, normally in 2
wire system, we will manual add/subtract some resistance
value with the measured resistance value.but it is no percise
whereas in 3 wire system, a parallely third wire run with
the two polarity wires, but its direction of current flow is
opposite to the other two. so it will cancel the line
resistance and give exact value. similarly, for more precise
and accurate measurement, we mostly use 4 wire system.
In above mentioned description, the addition of resistance
or removal of line resistance through extra wire is called
compensation for RTD
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / sandip patel
RTD means resistor temperature detector .its resistance is increase with increasing of the temperature. 2wire RTD is used for direct use of it but 4 wire RTD used when the compansation is needed in plant for removing the errors.
| Is This Answer Correct ? | 7 Yes | 11 No |
How to control flow variations in magnetic flow maters..... When i will provide proper earthing?
How is work 5/2 sov?
You are looking at the RS-485-side of an RS-232/RS-485 converter and the power supply voltage for the converter is +5V. Under idle conditions (no transmission), and assuming you have enabled the RS-485 output: what would you expect at: (a) Output A measured against output B (b) Output A measured against ground (c) Output B measured against ground
We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.
admittance level sensor meaning?
What is the purpose of LO Overhead tank in turbines.
What is i/e or o/p transmitter(ma/v)?
hi friends,can u send me the link for downloading Allen_bradley_RsLogix_500_Pro_V_7.0 software with activation file.or how can i find activation file for this.
Can anybody tell me how to select the size of earthing cable for DCS & PLC system.Please tell me any relevant answer here or mail it to me.
Why all the drains(Gland sealing,ESV,Casing inlet etc) are directly connected to the flash tank instead of hotwell of the condensor in the power plant? My Email Id:naba02222@gmail.com
How to calibrate Field bus transmitter? procedure ?
why magnetic flow meter is not used in thermel power plant operation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)