WHAT IS THE SPECIFICATIONS CONSIDERED DURING DESIGN FOR THE
OVER CURRENT RELAY?
Answers were Sorted based on User's Feedback
Answer / chinnaraj eee
While designing any type relay we have to consider only the
current through the operating coil of the circuit breaker
and NO & NC contacts of the relay. i.e, only it will sense
the current flow a.nd fed to circuit breaker which results
interrupting the current flow in the line.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / appurao. s
For the Over Current Relay, (Mostly CT operated)it will be considered the Ct secondary current either 1A or 5A depends on the system design. Mostly today's digital relays are having the option to select between the range.
Also the time for interrupting the flow of current when the over current phenomena arises. Time setting will be range bound, so that the user can decide.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / manoranjan mishra
While designing any type relay we have to consider first
the current setting of the breaker which is sensing to
relay operating coil.if it take more than its rated current
then it trips the relay which is connected to equipments.
| Is This Answer Correct ? | 0 Yes | 0 No |
BRIEFELY EXPLAIN MEGGAR PRINCIPLE
what is the purpose of slope in the differential relay?why we are using two slope?but in busbar differential we are using only one slope.why?
what will happen if the frequency supplied is more than the frequency of the instrument...?
why we use taping of transformer on HT side?
For an 100kw generator, only 50kw of load is connected. Will the generator generate only 50kw or 100kw. If it generate 100kw what happens to rest of the 50kw. What happens if we connect more than 100kw of load?
why extension in transmission tower is made?
what is conductor copnstant of ab cable
how i calculate the size in mm of the LT 4 core cable for 100 HP inductive motor pump
in 4 pole lap wound dc motor one brush is disconnected then what result in new voltage if its voltage is v volts power is p watts current is i amp
how to calculate Transformer loss?
what is the spdt
What is the output of 25 kva 11/.4 kv transformer in kw ? Plz generalized it...
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)