what are check points to be checked while charging
switchyard?(CT,PT,BREAKER,POWER TRANSFORMER)
Answer / arun 9865576777
Transformer Commissioning Work
Preliminary Test
1. HT Switchgear End
 HT BKR IR Value
Open Condition Closed
Condition
R-RI= R-Y=
R-E=
Y-YI= Y-B=
Y-E=
B-BI= B-R=
B-E=
2. Transformer end
 TRF IR Value
Note: - Neutral earth should be open
LV line PT fuse& earth link open
15sec 60sec 600sec PI
HV-E
LV-E
HV-LV
After the above tests put back neutral earth line pt fuse&
earth link Connection properly.
3. LV Panel End
 LT BKR IR Value
Open Condition
Closed Condition
R-RI= R-Y=
R-E=
Y-YI= Y-B=
Y-E=
B-BI= B-R=
B-E=
Preliminary Checks
1. HT Switchgear End
 Check Relay Setting
 Check Tightness Of CT TB
 HT Cable Connection
 Interlock Trial
 Stability Check
 BKR Trial In Test Mode
 Check Fuse
 Check MTR Operation
 Reset The All Relay
 Check Control Supply
 Reset Max Value On Relay
2. Transformer End
 TRF Body Earth
 TRF Neutral Earth
 HT Cable Connection
 Check Tightness Of CT TB
 Check WTI,OTI (or) Door Inter Lock Trial
 Check OTI,WTI Setting
 LV Side Flexible Tightness
 Check Marshalling Box Control Supply
3. LV Panel End
 Check Relay Setting
 Check Tightness Of CT TB
 LV Side Flexible Tightness
 Check Line PT Fuse
 BKR Trial In Test Mode
 Check Control Fuse
 Check MTR Operation
 Check U/V Trip Throw Line PT
 Reset The All Relay
 Check Control Supply
Before Charging
 Line PT should be in service
 LV BKR should be open condition
After TRF Charging
 Note Down Electrical Parameter In HT Side & LT Side
 Phase Sequence In LT Side
| Is This Answer Correct ? | 1 Yes | 1 No |
It is observed that AVR of an Alternator is more likely to fail if the Generator and Mains Neutral are directly connected to each other. Why should this be so?
Why Hg means mecuiry used in vaccum mesuring unit?
what will happen if dc is supplied in acb or mccb or other circuit breakers?
how does this job compare with others you have aplied for?
what is full form of dyn11( in transformer)
what is earth fault relay 64T, why it is used in main Incomer and neutral CT of Transformer.
what is a circuit breaker. Weite the types of circuit breaker.
why transformer are rated in kva.
when the size of the cable used for the ht voltage is 300sqmm then what is the size of the conductor of each phase
OHMS Law is only applicable for ac or dc or both circuiT?.
Why cables and busbar both needed in LT Panels?
i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)