what is full form of dyn11( in transformer)
Answers were Sorted based on User's Feedback
Answer / rajesh
wat the bleddy answer ...if u dont know u shouldnt post tat
worst answers.....
nw see answer...
its nt 5 degrees dear tat 11 means it resembles 11 o clock
in a wall clock tat means it makes 30degrees.......
so tats it ther is phase between primary and secondary of
30degree
THIS IS A COMMERCIAL NOTATION OF TRANSFORMER
| Is This Answer Correct ? | 21 Yes | 4 No |
Answer / anil
the first letter must be capital one, which represents HV
winding while second letter should be lower case, which
represent LV winding of transformer.
1. 'D' - HV winding is delta connected & 'Y'- HV winding
is star connected
2. 'd' - LV winding is delta connected & 'y'- LV winding
is star connected
And rest of number indicating phase displacement angle
i.e 1 = 30°, 2 = 60°, 3 = 90°, 6 = 180° and 12 = 0° or
360°.
so
Dyn11 indicates,
Delta connected HV winding, star connected LV winding with
neutral brought out, LV is leading HV with 30°
| Is This Answer Correct ? | 13 Yes | 1 No |
Answer / meenakshi
i agree vid anil...to b more specific,Phase rotation is
always anti-clockwise. (international adopted convention)
we use the hour indicator as the indicating phase
displacement angle. Because there are 12 hours on a clock,
and a circle consists out of 360°, each hour represents
30°.
Thus 1 = 30°, 2 = 60°, 3 = 90°, 6 = 180° and 12 = 0° or
360°.
The minute hand is set on 12 o'clock and replaces the line
to neutral voltage (sometimes imaginary) of the HV winding.
This position is always the reference point.
Because rotation is anti-clockwise, 1 = 30° lagging (LV
lags HV with 30°)and 11 = 330° lagging or 30° leading (LV
leads HV with 30°)
| Is This Answer Correct ? | 7 Yes | 1 No |
I correct my self it is a 30 degree phase shift.
Thank's rajesh for your inputs.
| Is This Answer Correct ? | 3 Yes | 2 No |
DYn11 Means D=Delta, Y=Star, n=neutral, 11= 5degree phase
shift. This means there is a phase shift of 5 degree from
primary to secondary of a transformer.
| Is This Answer Correct ? | 9 Yes | 20 No |
Why cant we connect the motor output to generator and then generator output to motor ?
which type of questions asking for solar companies?
On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.
when the rheostat kept in minimum to maximum position in motors what will happen?
HOW DG WORKS ?
how braking & making capacity of circuit breaker are calculated?
Hi, We have have the major losses between BBT ( Bus Bar Trunking) to LT Incomer & LT to HT incomer, how to arrive the losses?
why capacitor offer reactance to alternating current?
what is the difference between interconnection and intraconnections in the circuit diagrams
I have a 600VA UPS for computer only. It holds for 20minutes only. 1. Can it be upgraded for longer period.? 2. Can it be used for one ceiling fan and a tube light? If yes, how to upgrade?
Can we get the shock if Power system is unearth means delta type take an rated voltage as 6.6 KV?
What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)