i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible
Best regards
ikraam haider
Answers were Sorted based on User's Feedback
Answer / s.arunraja
Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels
Regards
S.Arun Raja
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sagar khandekar
First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.murugan
Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter
boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN
IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashish mahadik
U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.
Is This Answer Correct ? | 1 Yes | 2 No |
what is the Difference betwee the Hart and smart series Pressure transmitter
1 Answers HPCL Mittal Pipelines Limited HMEL, Kastech Instrumentation,
I am an intru engg frm pune n completing mba marketing in may 2010, what kind of profile would best suit my educational qualifications??? Also, i will move to US in jan 2011, so this job experience should count Over there too 'coz i want to continue workin even there....
what is intrinscily safe system and where we use?
What is eddy current? Describe the operating principle of proximity probe.
Difine flashing , Cavitaion & Noise? how to minimize these effects
what is solenoid valve?
What is Cavitation in a control valve?
Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.
how to callibrate a new i/p converter
difference b/w single acting and double acting actuator by using application only?
Describe the concept of Gain Scheduling, as currently found as an option in some controllers.
diff c and c++