i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible
Best regards
ikraam haider
Answers were Sorted based on User's Feedback
Answer / s.arunraja
Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels
Regards
S.Arun Raja
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sagar khandekar
First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.murugan
Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter
boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN
IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashish mahadik
U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.
| Is This Answer Correct ? | 1 Yes | 2 No |
explain key exchanges in all security modes WPA,WPA2,TLS?
what is difference between RTD , thermo couple and thermistor in general ?? (except temperature co-efficient )
Can we get the outpot in c without using getch fiction? Answer is yes but output will stay on display 4 only few second.... But can we get output without using getch and also output will hold on the display...?
whatis range of marcury filled tempereture gague
why 4 to 20 ma used at 0 set
1. How can leveltrol be installed in steam drum for measuring the level of steam drum?
How servomotor controls throttle valve of TURBINE?
what is the difference between active and passive loop ?
What is the purpose of bypass valve across AS valve.
What are the type of bonnets in the control valves?
how can we tune a PID. If it is by zeiger nichols method..please explain briefly with help of an example.
Can I calibrate the Electromagnetic Flow Meter on line and How.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)