Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible

Best regards

ikraam haider

Answers were Sorted based on User's Feedback



i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / s.arunraja

Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels

Regards
S.Arun Raja

Is This Answer Correct ?    4 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / sagar khandekar

First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.

Is This Answer Correct ?    2 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / r.murugan

Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter

boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN

IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING

Is This Answer Correct ?    1 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / ikraamh5

engineering level

Is This Answer Correct ?    0 Yes 1 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / ashish mahadik

U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

can anyone can let me know in Eurotron Micro cal 2+ calibrator in milli amps source mode we are not able to get 20 milli amps output it only produces 1.52 milli amps out, but display shows increase in milli amps , and err6 displays, let me know how to remove the err 6.

0 Answers  


In vortex flow meter how can measure the frequency of vortex generated by vortex flow meter

4 Answers   Cadila,


There are two chlorination tonners both are connected to two pressure swithes and the pressure switch is connected to SOV which operates the valve to changeover the tonner selection i.e if pressure one tonner goes low the other tonner should come in line if it is inautomatic selection design a circuit using relays ?

0 Answers  


what is sinking and sourcing....

2 Answers  


While giving Power Supply of 24 VDC to a Transmitter,why Shield Terminal is connected either at Transmitter or at ISB.Why not Shield Terminal connected at both ends.If the Reason is to avoid Noise interference,which type of noice that is interfering.Is the Noice from the 24 VDC supply terminals or from any external source.

1 Answers  


how i can copy paste the program of smart transmitter to another smart one with hart communicator?

2 Answers   KOC,


why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature

0 Answers   ABG Energy,


why do we use 4-20 ma current why cant o-20ma

6 Answers   Southwest Cheese,


How to check electrical health of Vibration probe?

1 Answers   QAFCO,


Why the industry's standard current standards are from 4mA to 20mA,not from 0mA or any other range?

3 Answers  


sir i m preparing for BARC but i am not getting any papers to prepare for this exam so please send me some sample papers to my i.d for the preparation of barc.

0 Answers  


What is solenoid valve? Where it is used?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)