i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible
Best regards
ikraam haider
Answers were Sorted based on User's Feedback
Answer / s.arunraja
Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels
Regards
S.Arun Raja
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sagar khandekar
First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.murugan
Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter
boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN
IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashish mahadik
U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.
| Is This Answer Correct ? | 1 Yes | 2 No |
you must show the examples application and give at least 4 types of transducer/sensors that can minimize the failure during the manufacturing of the resistors.
How to find out the current of two motors having same power consumption but different RPM?
What is the Working principle of Dozing valve?
Rtd sensor how to calibrate
Can we use twisted pair cable instead of ethernet for communication?
What is Cavitation?
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
Difference between ultrasonic flow meter and radar type flow meter
2 Answers Dodsal, Qatar Petroleums,
wht is snap action switch?where it is used?is there any diff between snap action switch and normal pressure switch?
EXPLAIN SOME IMP QUESTIONS AND ANSWERS ON TOPIC ELECTRONICS,INSTRUMENTATION.........
what is the differnce betweeen hart and smart tx
how to calibrate TT transmitter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)