i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible
Best regards
ikraam haider
Answers were Sorted based on User's Feedback
Answer / s.arunraja
Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels
Regards
S.Arun Raja
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sagar khandekar
First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.murugan
Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter
boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN
IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashish mahadik
U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.
| Is This Answer Correct ? | 1 Yes | 2 No |
can anyone can let me know in Eurotron Micro cal 2+ calibrator in milli amps source mode we are not able to get 20 milli amps output it only produces 1.52 milli amps out, but display shows increase in milli amps , and err6 displays, let me know how to remove the err 6.
In vortex flow meter how can measure the frequency of vortex generated by vortex flow meter
There are two chlorination tonners both are connected to two pressure swithes and the pressure switch is connected to SOV which operates the valve to changeover the tonner selection i.e if pressure one tonner goes low the other tonner should come in line if it is inautomatic selection design a circuit using relays ?
what is sinking and sourcing....
While giving Power Supply of 24 VDC to a Transmitter,why Shield Terminal is connected either at Transmitter or at ISB.Why not Shield Terminal connected at both ends.If the Reason is to avoid Noise interference,which type of noice that is interfering.Is the Noice from the 24 VDC supply terminals or from any external source.
how i can copy paste the program of smart transmitter to another smart one with hart communicator?
why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature
why do we use 4-20 ma current why cant o-20ma
How to check electrical health of Vibration probe?
Why the industry's standard current standards are from 4mA to 20mA,not from 0mA or any other range?
sir i m preparing for BARC but i am not getting any papers to prepare for this exam so please send me some sample papers to my i.d for the preparation of barc.
What is solenoid valve? Where it is used?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)