i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible
Best regards
ikraam haider
Answers were Sorted based on User's Feedback
Answer / s.arunraja
Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels
Regards
S.Arun Raja
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sagar khandekar
First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.murugan
Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter
boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN
IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashish mahadik
U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.
| Is This Answer Correct ? | 1 Yes | 2 No |
what is use of communication wire in multipare cable(oil and gas field), why this communication wire not used in single pair cable?
Why Ma signal is using for control system?
what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liquid density .73, transmiter fixed on a fractionation colum, under vaccume 10mbar
What is the difference in clamp on type and inline type ultrasonic flow transmitter.
How does temperature bath work? How does coil gets heated only by applying some current?
0 Answers Process Control Technologies,
d/p flow transmitter LP side give to pressure.what you geting out put ? how you get(ma)?
Q- Which of the following is Close loop system - a-)respiratory System b-)traffic light system c-)washing machine d-)Room heater my option is A, what is our take on option B & C
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
How to Calibrate Transducers? Can you give me a step by ste procedure?
What are the different types of thermistors used in industries? How to the operation of typical thermistor?
why is an oxygen sensor used in a boiler stack
I am an intru engg frm pune n completing mba marketing in may 2010, what kind of profile would best suit my educational qualifications??? Also, i will move to US in jan 2011, so this job experience should count Over there too 'coz i want to continue workin even there....
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)