While giving Power Supply of 24 VDC to a Transmitter,why
Shield Terminal is connected either at Transmitter or at
ISB.Why not Shield Terminal connected at both ends.If the
Reason is to avoid Noise interference,which type of noice
that is interfering.Is the Noice from the 24 VDC supply
terminals or from any external source.
Answer / carl_ellis
1) A shield (screen) connected at both ends will carry
ground loop current due to the difference in ground
potentials at each end. A shield (screen) carrying current
will induce noise into the wires it is shielding.
Historically, shields (screens) have been connected at one
end only, typically at the receiver
(DCS/PLC/PAC/RTU/controller) end.
Current thinking as outlined in IEC 61000-5-2
Electromagnetic compatibility (EMC) - Part 5 Installation
and mitigation guidelines - Section 2: Earthing and cabling,
recommends grounding the shield at each
end for point-to-point and at every point for multi-drop.
Two point grounding provides protection against EMC and for
safety as well. However, this method assumes that all
points are on the same ground (i.e. use an equipotential
grounding grid).
Typically, Siemens has adopted this recommendation for
Profibus DP, an RS-485 multi-drop network. Of course, the
gotcha is "all points at the same ground potential". Not
in the real world, Mr. Siemens.
2) Although 24Vdc power supplies can be noisy, major
manufacturers produce DC power supplies with very little
ripple and excellent regulation.
DC power supplies used for HART need to meet the HART spec:
Maximum ripple (47 to 125 Hz) = 0.2V p-p
Maximum noise (500 Hz to 10 kHz) = 1.2 mV rms
Maximum series impedance (500 Hz to 10 kHz) = 10 ohm
24Vdc power supplies are not typically the source of noise
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
define SIMULATION a and what is the need of it
What is difference between converter & transducers?
Difference between ultra sonic flow meter
Explain, and give a real-world example of MODULATING control
What unit is used for measuring comp. outlet flow. it is CFM, M3/hr or NM3/hr. ?
how the transmitter send MA?
What is the cv of a control valve?
What is glanding
1)What is the suitable MOC for flow meters working at temperature between 200 - 250 cen. 2)In which application the mass flow meters are not advisable 3)Is it advisable to use radiation type or radar type instrument for non contact application
what is puling in n pulling out in flame scanner system?
Identify and use the ANSI/ISA-S5.1 consensus industrial standard process symbols.
why cant we use mV instead of mA?
12 Answers ABB, Power Grid, Qatar Gas, USW, Visa Steel,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)