If a Power Transformer Fails and the transformer
manufacturer suggest that "Do all electrical test on the
transformer?".
What are the test to be conducted in this condition?

Answers were Sorted based on User's Feedback



If a Power Transformer Fails and the transformer manufacturer suggest that "Do all electrical..

Answer / satya dev

electrical test to be performed are as under.

1- Magnetic balance test.
2- Megnetising current test.
3- Turn to turn ratio test.
4- Vector group test
5- Knee point test
6- Winding ressistance test( Phase - Phase - Eatrh)
7- Meggering of bushing.
8- Tan Delta test.

All test must be performed after disconned to the
transformer from the Input & output supply.

Is This Answer Correct ?    9 Yes 1 No

If a Power Transformer Fails and the transformer manufacturer suggest that "Do all electrical..

Answer / k.prakashchandra

You can conduct tests with the instruments available with
you.If you entrust it to a private firm to conduct all the
tests ,they will charge you about Rs 20,000/-.As you are not
supposed to open the Tr and apply any substantial
voltage.The following tests will be sufficient.1. Insulation
2.continuity 3.bdv of oil 4. winding resistance(with
sensitive ohm meter) .These together with relay operations
will give some idea to the manufacturer.You can conduct
ratio and magnetic balance tests with great care if IR and
bd values are satisfactory.

Is This Answer Correct ?    0 Yes 0 No

If a Power Transformer Fails and the transformer manufacturer suggest that "Do all electrical..

Answer / satya dev

Dear Mr. Praksh I am agree with you but all the above test
details which given by me is for high rating power
transformer & it must be carried out and Rs 20 K does not
matter with respect to cost of transfromers.

Is This Answer Correct ?    0 Yes 0 No

If a Power Transformer Fails and the transformer manufacturer suggest that "Do all electrical..

Answer / k.prakashchandra

Test No. 1 and 8 belong to life evaluation tests.As the tr
has been in use, tests No. 4 and 5 may not be necessary.For
Inter-turn short, test No .2 may prove useful if the
previous values are available and magnetic balance test (
No.1 )is really useful.Oil test is just for knowing the
present condition.If the tr has failed within the guarantee
period , we have to take extra care while furnishing the
test results. The firm may put the blame on you,for the
damages for applying the voltages to test.Simple tests and
relay operations are sufficient.It is more difficult to
prove that a tr is healthy by all means.

Is This Answer Correct ?    0 Yes 0 No

If a Power Transformer Fails and the transformer manufacturer suggest that "Do all electrical..

Answer / k.prakashchandra

Let me cite an example.We have one 220/110 KV 100 MVA Auto
transformer.After 5 years of service ,it tripped with a
sound, on the following relay
indications.Diff,OS,Bucholtz,OC -R ph and EF (REFR not
provided).On meggering without test charging ,the results
were OK with LT R -body being higher.Then we resorted to
continuity test ,which indicated that LT R phase bushing
has been open circuited.On examination it was found that
the joint in the lead from R-phase winding to bushing was
severed due to bad workmanship.We did not conduct any other
tests.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

WHY CAN WE NOT CHAGE SPEED OF SYNCHRONOUS MOTOR...............................JUSTIFY

2 Answers   ISMT,


how DC motor operating in detail .pls any one guide me .iam not clear idea about that .thank u

2 Answers  


for any load, what happen if we use the cable rating above its normal rating

2 Answers  


I want to know Electrical Circuit?

0 Answers  


Why the isolation treasforfer are connected at out put of the ups ig 200kva ??????????????????

3 Answers  






What is meaning of Float Charging of Batteries???

2 Answers   Emerson,


What is an exciter and how does it work?

7 Answers   FCUK, Lotte Chemical Titan, TATA,


What is mean by % impedance of transformer? detail explanations expected.

1 Answers   FCUK,


How to solve the problem of low voltage at consumer end in distribution system if one phase come low voltage of transformer

1 Answers   ABB,


If Three Runs of 1Cx300 Sqmm Cable between Transformer and VCB and the distance between 100mtrs. what will be total length of Cable and if cost 1500Rs per meter,what would be the total cost

1 Answers   ANITS,


What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?

0 Answers   JKN Limited,


Dear all i want to know SEWA Electrical Supervisor Licence test Previous Year Questions ? If any body know please send to me zohairaukllah@yahoo.com

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)