If one d.g. is unable to take full load of system, then
second d.g. will take care of partly Load.for this
condition RPM of both DG set should be equal.By using
Synchronization panel RPM of dg sets are match, is it true?
Answer / vinoth
For Synchronisation the following parameters needs to be matched,
*Phase voltage
*Frequency
*Speed(RPm)
In auto operated DG sets the GCP will take care of matching this parameters, In manual operated DG sets there is an option for matching the Phase voltage and frequency(i.e joystick to adjust voltage and frequency).Since the RPM is depends on the first two factors, the speed will be matched if the first two parameters are same.
Is This Answer Correct ? | 2 Yes | 0 No |
what is the principal of starting of a three phase induction motor.
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
What is different between DOL(Direct on line starter), VSD, S/S(Soft starter), and A/T(Auto Transformer)
What is the difference between Droop vs Isoch Control?
How much costly in percentage wise is sandwich busduct costly than air insulated busduct of any rating?
How to check the efficiency of the generator , air compressors.
What is dynamo?How it works and what is the function of dynamo in a DG.
how to carried out tan delta test in 11 KV alternator ?
why voltage coil in wattmeter called as pressure coil why the pressure term is used in wattmeter?
what is the per unit cost of generation of electricity at thermal,hydro,desael,solar,gas power plant
why so voltage is same in parallel circuits and current is same in series ckt?
WHAT IS METHOD TO DESIGN SIZE OF A 11KV UNDER GROUND CABLE FOR A OUTGOING FEEDER FEEDING 6NOS 250KVA TRANSFORMERS WITH 5KM LENGTH OF FEEDER?