What is maximum demand?How can we caluclate it?
Answers were Sorted based on User's Feedback
Answer / natha
on the basis of load curve it is calculated.if suppose you have to find the max demand(md)of ur house plot time on x axis units consumed on y axis.you get supppose 2units 6am 30 7am 42 8am 5 9am.....till midnight.then ur max demand is 42units.all other factors such as load factor,diversity factor can be found.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shamsher singh
the maximum demand is the plant maximum load allow the state
electrical board on 500 kva we can use the load inside the
limit that in sanction load by the state electrical board
for a example our transformer is 500 kva and according
to power factor we calculate in standard 500*0.9=450kw .we
authorized only 450 kw only.govt authorized me only 450 kw
we cross the limit we pay the penalty
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / lohith
75 percent of the
contract demand.
Its multification
factor is cubical
meter ct ratio into
pt ratio
| Is This Answer Correct ? | 0 Yes | 1 No |
Can anybody tell me how to calculate(formula) earth flat size(for copper and aluminium).
What's is the difference between IVT and CVT?
Hi, what is 100 % stator earth fault protection and how it can be achieve by 3rd harmonics and low frequency injection principle ?
what is the difference between high impedance and low impedance circuit?
at work we have a 3 phase motor but on testing one phase isnt getting a reading. it runs 24 hours a day all week. stops and starts well no noise or heating. the phase isnt down to earth.is it just a bad meter reading or not? phases one and three came up with a resistance reading of 0.4 but phase 2 couldnt get anything shows up as open circuit.
in communication what is the role of elelctrical engineer?
What is Instantaneous Earth fault relay,how will work
How induction stove works?
For a 50MVA (138/69/13.8 KV) transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.
what is the working principale of air circuit breaker ?
The formular of how to calculate a cross sectional cable to feed an electric motor. Examle: 15KW, 26.1A, 415V. Calculate the cable size in mm2
what is difference b/w HT & LT and the range of HT & LT ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)