What is maximum demand?How can we caluclate it?
Answer Posted / shamsher singh
the maximum demand is the plant maximum load allow the state
electrical board on 500 kva we can use the load inside the
limit that in sanction load by the state electrical board
for a example our transformer is 500 kva and according
to power factor we calculate in standard 500*0.9=450kw .we
authorized only 450 kw only.govt authorized me only 450 kw
we cross the limit we pay the penalty
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
what is the common earth
what is servo motor and how it works?
how many electricity poles are there and what are the names and their sizes.
describe the constructional features of an auto transformer and its principle operation
How to design harmonic filter at the project stage without nowing the harmonics levels
what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY
if in 3-phase system voltage=440V,frequency=60Hz, current=400A. then if it is single phase then current=? and if it is single phasing then current=?
transformer phasor diagram under load explain it?
how to avoid Saturation in C.T?
some time we open engine breaker 8.0 MW load but plant not trip. and another time engine open 4.0 MW load engine trip why? individually engine breaker open & individually emergency stop why difference?
How to calculate phase to phase difference ?
why we used dc supply for field in dg set
Minimum IR value of 1.1 kv grade 3.5c (300, 240,185,150,120,95,70,50,35,25) sqmm Aluminium XLPE cable and 4c (16, 10,6 & 4) sqmm cu arm cable between RY,YB,BR,RN,YN,BN,RE,YE,BE & NE.
what is the meaning of number in (11, 31, 61,14, etc. CDG11, CDG31, CDG61, DDT32
I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.