Answer / r. anand
VFD(Variable frequency Drive) is a type of AC Drive.
There are two types of AC Drives of this category,
VVD (Variable Voltage Drive)in which the speed of the drive
can be controlled by varying the voltage input to the drive.
and
VFD (Variable Frequency Drive)in which the speed of the
drive can be controlled by varying the input frequency to
the drive.
| Is This Answer Correct ? | 18 Yes | 6 No |
Answer / mr. vinayak manohar hawal
AC drives control the speed of either an induction
motor or a synchronous motor by adjusting the frequency of
the power supplied to the motor.
AC drives are also known as adjustable speed drives
(ASD) or adjustable frequency drives (AFD) or variable
frequency drives (VFD) or variable speed drives (VSD) or
frequency converters (FC).
So I think that VFD is basicaly a method of AC drive
used for changing the speed of motor.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / comil83
Both are same.Now a days most of company like
siemens,ABB,yaskawa..etc provides diffrent types of control
in drives like 1) v/f control with feedback 2) v/f control
without feedback 3) vector control with and without
feedback.
In v/f control u can varying speed with the help of v and f
but u can not control torque and in Vector control u can
control speed as well as torque.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / gautam himmatramka
But generally the concept of drives is that the ratio of
Voltage to freq. should be constant at each instant of
operation of drives. So i feel AC drives are a genral term
with VFD as a more specific name of the same.
| Is This Answer Correct ? | 2 Yes | 0 No |
Both are same. comman name in Ac drive. In that by logic we
can segregate Vfd(variable freq. drive) VVd(variable
voltage drive).
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / suresh pethe
AC drive -- Variable voltage
VFD -- Variable Freqency
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prabhakar jha
in vfd controlled speed & current by variation of frequency.speed & current directly proportional of frequency ...
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rajesh jagtap
Actually AC Drive means a controller which require
Alternating Current power source and VFD means controlling
drive by varing frequency.
| Is This Answer Correct ? | 1 Yes | 2 No |
in VFD you can vary the speed according to flow hense power
is consumed acoordingly
in AC drvies the speed of the motor remains constant
whatever the speed you cant vary the speed.
| Is This Answer Correct ? | 10 Yes | 16 No |
ohms law is applicable for dc or ac current or for both??? explain it berifly??
Procedure for conduting vector group test on power transformers.why it is conducted?
What is the criteria that generally follow by distribution licenses to fix contact demand of their industrial customers?
DIFFERNCE BETWEEN DCS AND PLC? HOW IT WORKS?
what is the diffrence between mcb &elcb?
WHAT CAUSED THRESHOLD VOLTAGE TO EXIST?
What is the importance of quality factor in resonance?
1 Sq.mm ( Aluminium Cable ) = How much Amphere ( AMP )
how to decide the ratings of the busbar in electrification.give me the proper thumb rule or procedure
Why design 150Hz in Exciter
HOW GENERATING END VOLTAGE LEVEL (6.6 KV/ 10.5 KV/ 11 KV/ 13.5 KV) DECIDED IN POWER PLANT. ON WHAT FACTORS THE GENERATING END VOLTAGE DECIDED, & WHAT IS THE CALCULATION USED FOR THIS.
How to work meggar?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)