what are ABCD curves in MCBs and how we observe that curves?
Answers were Sorted based on User's Feedback
Answer / raja
Type B :
MCBs react quickly to overloads, and are set to trip
when the current passing through them is between 3 and 4.5
times the normal full load current.
Type C :
MCBs react more slowly, and are recommended for
applications involving inductive loads with high inrush
currents, such as fluorescent lighting installations. Type C
MCBs are set to trip at between 5 and 10 times the normal
full load current.
Type D :
MCBs are slower still, and are set to trip at between
10 and 20 times the normal full load current. They are
recommended only for circuits with very high inrush
currents, such as those feeding transformers and welding
machines.
Type A:
i have no idea on it
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / janet roadway
There is no A curve type within the IEC 60898 product
standard. The standard curves are B, C and D
Type B :
MCBs are set to trip when the current passing
through them is between 3 and 5 times the normal full load
current. The calibration temperature of this full load
current can vary from manufacturer but is generally in the
region of 30 - 40 degrees Celcius to allow for the heat
generated by the MCB within a distribution board.
Type C :
MCBs react more slowly, and are recommended for
applications involving inductive loads with high inrush
currents, such as fluorescent lighting installations. Type C
MCBs are set to trip at between 5 and 10 times the normal
full load current. Temperature as above
Type D :
MCBs are slower still, and are set to trip at between
10 and 20 times the normal full load current. They are
recommended only for circuits with very high inrush
currents, such as those feeding transformers and welding
machines. Temperature as above.
Some manufacturers produce their own specialist curves -
such as the ABB 'K' Curve which are designed for specific
applications such as tranformer feeds and motors. These
curves can be very useful.
| Is This Answer Correct ? | 1 Yes | 0 No |
State magnitude criterion.
While starting a high capacity motor, it takes 6 times the full load current. Why it doesn't trip relay or CB's in that network?
how to find the ballast lost from the actual wattage? for example i am going to buy decorative type 2x36watts fluorescent light fitting for this lamp how to find the ballast lost? is there any formula?
What are the types of circuit breakers ?
at what base you will tell the direction of rotation of dc motors and generators?
why is control bus bi-directional?
what is reactive power is it good or bad for a system
What is Phase margin?
what is diffrence between dc motor and dc generator?
what is the main difference b/w contactor and relay
2 Answers Pace Pharmaceuticals,
what is the diff.between neutral and earth?
it is clear that volts equal to the current as per ohms law. is it appliable to the AC power or only for DC. if it is appliacable to AC in transformers when voltage increases the voltage decreases ????? why??????????????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)