Answer / s kannan
MF is not for panels for relays and meters only. Meters will be connected with CT and PT's secondary. If we want to calculate MF for meters like Voltmeter and Ammeter Just follow the formula Mf= CT Ratio X PT Ratio.
Eg:
CT Ratio: 600-300/1-1A(Adopted ratio is 300A as primary) PT Ratio: 33KV/rt3/110V/rt3/110V/rt3
Then MF:(300/1)X(33000/rt3/110/rt3)
(300/1)X(33000/1.732X1.732/110)
(300)X(33000/110)
(300)X(300)
90000
Means Multiply the particular meter's reading by this 90000 for obtaining the genuine value.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the effect of vector group while phase sequence of a generator changes,whether the vector group changes or not
What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???
How the power factor is more in high speed machines
Difference between auxliary relay & pla relay
How much energy save vfd if motor run on 50 Hz (full speed)
what is the method of earthing of a transformer using electrodes?
WHAT WILL HAPPEN IF INPUT SUPPLY OF RCBO IS CONNECTED TO OUTPUT SIDE
WHAT IS FORMULA TO KNOW TO BACKUP TIME OF POWER PLANT 48V/50AMP DELTA POWER PLANT
What is the limitation of kirchoffs law?
ynchronous M/C with under excitation with reactive power absorption , acts as a) synch. Motor b) synch gen c) synchr capacit
Why front mounted CT polarities are always towards breaker?
If the primary side current of 33/11 transformer is 64 amps then what will be secondary side current?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)