What is the effect of earth capacitance
Answers were Sorted based on User's Feedback
Answer / mahmood ahmed
Earth affects the calculation of capacitance of three-phase
lines as its presence alters the electric field lines.
Usually the height of the conductors placed on transmission
towers is much larger than the spacing between the
conductors. Therefore the effect of earth can be neglected
for capacitance calculations, especially when balanced
steady state operation of the power system is considered.
However for unbalanced operation when the sum of the three
line currents is not zero, the effect of earth needs to be
considered.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / abbas
what is effect of earth on three phase line capacitance?
Is This Answer Correct ? | 2 Yes | 0 No |
why we use bare wire in high tension power instead of using insulated wire?
1.25 kg of hydrogen are burnt with stiochiometric air, the mass of air in kg required is
What can make the the overloads operate when a star delta three phase motor starts?
What is the capacitance values of 132,220,400 & 765 kV current transformer
WHAT IS LINE TRAP,HOW IS IT FUNCTION?
We are planning to synchronized DG's with our captive plant in the event of black start of plant, but before sync we checked voltage of DG with our plant voltage and it varies from 5 V to 450 V. So in this condition how we can sync DG with plant ?
How many points does a Circuit can have?
Why synchronous motor is used in power factor improvement,dc series in lift
resitance in ac=1.6*resistance in dc
sir iam a 3rd yr eee student.no core company comes for recruitment to our college.my aim is to be placed in l and t.tell me the procedures.
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
What is the importance of quality factor in resonance?