Why voltage regulation of an alternator is negative for a leading power factor?
Answers were Sorted based on User's Feedback
Answer / arijeet chakraborty
In case of leading load that means capacitive load, the effect of armature flux on main field flux is magnetising i.e, the armature flux is adding up with the main field flux. Since it is adding up, the total induced emf(V) will also be more than the induced emf at no load(E).
Therefore voltage regulation= -ve
Is This Answer Correct ? | 56 Yes | 1 No |
Answer / md al mamun
in case of leading power,terminal voltage will fall on removing the full load,in this case voltage regulation is negative.
Is This Answer Correct ? | 15 Yes | 5 No |
The Gen voltage is less than the system voltage and gen
voltage rises to be equal instead of dropping due to the load
Is This Answer Correct ? | 7 Yes | 12 No |
what is a,b,c,d checks diesel generator?
how does commutator convert a.c to d.c?
0 Answers NRSC National Remote Sensing Centre, RBC,
what is the calculation of power factor?
Sir, why generating power plant operating at above 0.9 lag? detail explaination?
in three phase it represented by R-Y-B.what is full form of R-Y-B.
how the inner and outer body is separated in aircrafts?
why we use to transmit the power in three phases intead of single phase ?
what is MFD value in capacitor?I have 201 Kva load & reactive power is 150 Kvar. so how it is calculated?
Whats meant by trivector meter where it is connected at the substation?
20 Answers GPIL, Infosys, Jakson, L&T, Secure Meters,
Why is negative feedback invariably preferred in closed loop system?
What is the disadventage of gland earthing(power cable) if any. ?
How to Calculate KA Rating of Main LT Panel