If the t/f capacity is 500KvA then what is Amps ratting of
the main breaker.
Answers were Sorted based on User's Feedback
Answer / athar abid
As we Know that
KVA = Sqrt 3 . Voltage(V) . Current(I)
Now for 400V (Phase-Phase) syayem
I = 500KVA/(1.732 * 400)
=500*1000/(1.732*400)
=721.7 Amps
There is no standard breaker available with this rating, so
take one step above rating i.e. 800Amps
Hope its clear.
Regards
Athar Abid
| Is This Answer Correct ? | 1 Yes | 1 No |
What should be value of Circuit breaker operating time and tripping time?
What is the physical significance of phase.. i.e. what is exactly the meaning in layman's language.. 1 phase, 3 phase etc ???
what is the difference between earth and neutral?
wat is the role of reactive power in power generation?why we have maintain it.
Explain about how is it working Earth fault'relay and wahts the resistance value of earth bed
What is difference between incomer & outgoing type Vaccum Circuit Breaker?
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
what is closing resistor in circuit breaker? why it used?
what is the principle of the single phase energy meter? and,what is the advantages and disadvantages of single phase energy meter?
Comment on the working principle of operation of a single-phase transformer.
How the line trap works in substation...?
Did RMU have ct and pt ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)