Answer / rishi
first of all who told u that main and transfer bus is not used in 400 kv substation.This scheme is used in many substations.
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / naresh.devarakonda
one and half breaker scheme is more reliable, simple
operation and reduces the no. of isolators, bus.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / furqan ahmad
in one and halfbreker scheme scheme both breaker and bus
maintenance is possible.even though this scheme is costly
as compared to other schemes but becoz of reliability and
redundancy it is usually used for 400 kv switchyard
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jkrocks
DMT scheme is used earlier in 400kV System but all new 400kv ss are made on one & half breaker scheme. it has many advantages over DMT scheme.
more reliable than DMT each time line or ICT remain connected through both buses I & II, reduces numbers of confusing isolator in system, reduce additional bus.
If one bus trip due to any fault , lines are transformer connected to that bus remains charged through another bus by means of Tie CB.
Only disadvantage is that this system require three breaker for 2 lines or transformer.
But It is nothing against lots of advantages of One & Half Breaker Scheme.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / teju
one and half circuit breaker scheme is more reliable than
other schemes, simple operation and reduces the no. of
isolators, some electrical parameters & it is easy to handle.
Is This Answer Correct ? | 0 Yes | 4 No |
why transformer rating comes in kva?
what is the difference between Inverter and ups
explain how to protect high rise building from the risk of lighting.
how to calculate busbar capacity for 1000Kva transformer having22/.433V
2 Answers Electrical Tech, L&T,
What is the minimum permissive IR value for LT & HT motor for safe starting?
State the frequency for rc phase shift oscillator?
what happened if power factor is "1"
why we use taping of transformer on HT side?
how to calculate the cable size
What is the recommended voltage gap between Live and Earth and ,Earth and Neutral.If these are exceded what is the solution.
what is function of pump in DG?
how we could know that generator running anti clockwise with seeing the rotating direction of prime mover or engine