A powerplant has 8 gensets operating in grid parallel
mode. In one genset sometimes there is pf variation and kvar
variation. The plant operates in pf mode. When this
variation is onbserved the load is stable, voltage is also
stable, freq and genset speed is also stable. How will you
check the functioning of pf card. What shall be the ideal
output vdc of the pfc, from there it is input to AVR?
When it is in parallel with 7 other generators , its voltage and frequency(speed )are decided by the grid . hence its pf card is faulty as there no variation in shared load. Exchange the pf cards and confirm
| Is This Answer Correct ? | 0 Yes | 0 No |
draw singleline diagram of star to delta and dol starters
What are dependent sources?
Why we use the D-curve MCBs in critical power distrubution.
what composit error,ratio error,phase error in CT and PT??
PLZ EXPLAIN CORONA,SKIN,BIRD PALE,SPAN,SAG Effects of power cable.
Difference between 3.5 core and 4 core
is there any device that works properly accept relay, it may be fuse but if i want fuse of 33kv 300 amp it is avaliable, pls give me details
earth also having a gravitational force (magnetic field of north and south)but it attracts any object compare to this theartifical magnetic cant perform same as earth why?
what should be the motor rating for pumping water for house hold use from 60km far lake and what formula is to use please tell me
Differentiate AC and Dc resistance
how to make an earthing certificate
can any one suggest paper presentation topies for electrical engg?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)