why current coil has less number of turns compared to
pressure coil?
Answer Posted / anindita
current coil is connected in series with the load whereas
pressure coil is connected parallel to the supply, that is
pressure coil is connected across the voltage source.
current coil have lesser number of turns than the pressure
coil so that the impedance of the pressure coil increases
and it draws minimum current from the circuit,causing lesser
error in the reading.
| Is This Answer Correct ? | 22 Yes | 6 No |
Post New Answer View All Answers
Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.
lenz law application and define
What is slip in an induction motor?
How do i right a ladder diagram that has 1 actuator that performs a full stroke followed by a half stroke
If one tertiary phase i.e. R,Y or B is earthed of a loaded type tertiary delta connected (Without load)of a power auto transformer, what is its advantage/disadvantage?
explain remenance . differentiate high remenance type ct & low remenance type ct
what is submersible pump?what is different between motor and sub motor?
in HT service 3ph 4 wire service Y-phase voltage shows zero . whether it is meter fault? or what be the reason ? if y-ph voltage zero ,can current is recorded? reasons for failure?
what is the formula for efficiency of francis turbine and generator for hydropower? what is best way to select francis turbine and generator?
Can any body tell me the different types of LT cables & their application.
what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?
What is mean by hot and cold loop testing?
What happen to generator if i have unbalanced load?
what happen ehen synchronisation is done at below rated speed
Why let through energy not considered for ACB breaker while cable sizing?