What is the Different between CT Class-0.2 & Class-0.2s ?
Answer Posted / rao
For 0.2 Class specified accuracy is 'defined' between 5% to 120% of rated current, whereas for 0.2 S the accuracy is provided between 1% to 120% of rated current. At these secondary current ranges, accuracy is applicable when the burden is between 25% to 100%.
| Is This Answer Correct ? | 1 Yes | 1 No |