What is meant by line losses, how do you prevent the losses?
Answers were Sorted based on User's Feedback
Answer / r. anand
Line loss means power loss occuring during transmission of
Electric power. It is mainly due to copper loss(I2R). The
best way to reduce this is by increasing the voltage by
using a step up transformer, because when stepping up the
voltage, current decreases proportionatily. when I
decreases, I2 also will. Thus altogether I2R will decrease.
| Is This Answer Correct ? | 18 Yes | 1 No |
Line loss means loss due to I2R effect. That is the heating
loss in the transmission line. It is equal to Current
square multiply by resistance of total line.
It can be reduced by reducing the resistance of the line
ie. by increasing the diameter of wire. Or by sending the
same wattage, reduce current and proportionally increase
the voltage.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / ram t shelke
line losses can be divided as 1) copper losses 2) reactive
power loss 3) corona loss. copper loss mostly depends on
current flowing through the line & resistance of the
conductor.so try to keep these two values to minimum by
increasing system voltage& selecting proper size conductor.
reactive losses can be reduced by managing line loading
nearer to SIL conditions.the corona loss can be reduced by
increasing conductor size or using hallow size conductors.
| Is This Answer Correct ? | 1 Yes | 2 No |
Difference between megger test equipment and contact resistance meter test instruments?
what is the role of energy meter in distribution system ?
How the size of transformer decreases if we increases the frequency?
how to measure the voltage drop in cables also give formulas to calculate.
What are the types of windings according to the construction?
I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?
from which subjects most of the technical que will b asked for hpcl(electrical).pls help me
Sir, plz tell me the relation b/w KW and frequency in Variable frequency Drive?
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
What happen if 200 KVAR capacitor connected to power continuesly?
simple way to find busbar sizes??
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)