What is the difference between an ELCB and a RCD?
Answers were Sorted based on User's Feedback
Answer / raghavendran r
ELCB stands for earth leakage CB.It trips any faulty circuit
by detecting the current flowing through the neutral.Under
normal condition, the intensity of current flowing through
the neutral must be the same as the current flowing through
phase to load then to neutral.If the intensity is not the
same then it means that the return current is deviating from
its actual path ie flowing through equipment body or if the
current is not returned properly.Now consider a case where
the return current is flowing through a operating persons
body(electrocution) after coming out from the load.
In this case, ELCB will not work because the return current
intensity flowing through the persons body is same.These
were the draw backs in older type of ELCB.
To over come this draw back RCD ie Residual Current
Detectors are used along with the ELCB which detects the
residual current deviation ie in case of any electrocution
also and then trips the Circuit.
To detect any
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / pramod sharma
ELCB - ELCB STANDS FOR EARTH LEAKAGE CURRENT BREAKER.
RCD - RESIDUAL CURRENT DEVICE.
Is This Answer Correct ? | 0 Yes | 0 No |
What are pre paid energy meters ? How it works ?
What happens when ac supply is given as excitation voltage instead of dc supply
What is the approximate value of stacking factor?
How do you select a cable size(Cu & Al) for a particular load?
Why relay connected R phase and B phase.?
_____hamari_____tumhari____ne dil ki_____utari. _____ne ____ dekha ashe ___ doshti ko lage na hamari.Complete pajal
1 Answers Microfine Industries,
What is the difference between KW & KVA ?
Give two basic speed control scheme of dc shunt motor?
how meger function
electrical resistance in human body?please dedails quick. mail.psrinivasan20@yahoo.com
what is the role of impedance in transformer?based on secondary f.l.current(139 amps) and impedance(4.07) of 415/415v of 100 kva transformer. what is the primary current?
My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?