How to calcualte the total number of cells required for
particular UPS of some X KVA with 3 and 5 hours back-up?
Answer / maksoodazhar@gmail.com
24v×100ah= 2400 watt hr
Backup time = 2400/total load
= 2400watthr/1kva
= 2400/1000×.8
= 2400 watthr/800 watt
= 3 hr
Is This Answer Correct ? | 1 Yes | 0 No |
why insulation cost is more in underground cable than in overhead line?
where to use CT and PT?
WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION
What is the Levels of High Voltage, Medium Voltage & Low Voltage?
I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A
what is the full form of ka (100A mccb KA)
when a pure dc signal is sent through a moving iron meter, what will it read?? dc or rms?? when a variable dc signal is sent through a moving iron meter, what will it read?? dc or rms??
HOW MUCH CURRENT CAN A 3 -1/2 CORE 100 MM WIRE CARRY
Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue
why rotor winding in induction motor is not earthed. normally we uses star winding in rotor .why?
3 Answers Anglo Platinum, TATA,
How to use earthing on shipments.
how to select electrical equipment such as fuse,dg,transformer,motor,msb,wire,cable as per the connecting load..please mention any books to design,take licence