my question is Megger of cable insulation or swgr board
meggerring some values in one day 50mohms,some other day
checking different values(20Mohms).
this tell that some person tell that that values ok.
how to identify the megger value is correct.
pls tell me the answer.
Answers were Sorted based on User's Feedback
Answer / akhil.goyalanager1985
the megger value show the dielectric strength of the
insulation .through megger we conclude that the
deterioration of the insulation. & the value of megger
shoulb be greater than
2*kv+1=Mohm
As per therotical point of view .
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mukesh thakur
if you are asked to charge a m/c urgently, you can go for dummy charging using 3-phase load through a, say 16A MCB, and if the MCB does't trips then there is no problem you can go for permanent charging.
Is This Answer Correct ? | 0 Yes | 2 No |
How to calculate motor current for 3 ph & 1 Ph motor from KW rating?
what is the reason for balance of voltage in magnetic balance test?
Tell me the reason of connecting domestic t/f primary in star or delta,and also secondary side.
What is the difference between grounding & earthing?
How do ACB are maintenance, what are the problem occurred in ACB
What are the difference between normal application Transformer and Solar application Transformer?
what is the difference between electrical choke and electronic choke?
How can we design MEP services for Commercial Building in area about 22 Acres of land?
Why is reating of t/f in kva but for inverter in kw ?
which element is neglected during fault calculation? a)resistance b)inductance c)capacitance d)reactance
HOW TO CALCULATE BATTERY BACKUP TIME & AH CAPACITY AGAINST UPS KVA RATING?
how to find diesel consumption of 600kva DG per hours????