does the power factor of an induction motor improve upon
used in parallel with a synchronous condenser , used
commonly to provide a leading kva ?
Answer / rakesh
when a synchronous condenser is used in parallel with an
induction motor ( which normally operates at a low pf at
light loads) then the power supply to which an induction
motor is deriving its power from is relieved of providing
reactive power to im , while the im still draws the same
reactive power as before , the necessary kva is now
provided by the condenser as it exports reactive power.
hence the pf of im remains the same but the pf of the
combined system of im and sc is improved .
Is This Answer Correct ? | 5 Yes | 0 No |
how to calculate the power loss of cable?
how to calclate fault level
Is it required to lay GI wires along with GI/MS conduits from one point to another point though separate earthing cable is conncted from DB to Socket?
What is the function of wave trap in an electrical substation?
If auto trip is operated, can you close the breaker.
What are the effects to a distribution transformer rated 10Kv with ratio 10Kv/0.433Kv, 3phase 50hz for example but fed with power supply of 11Kv?
A transformer has negative voltage regulation when its load PF is A zero B unity C lagging D leading
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
Hydro P.P. run @ 600 rpm,8pole, Nucler P.P @ 1500rpm 4 pole , ThermlP.P @ 3000 rpm 2 pole.Why this diffrence??? when we can generate electricity @ 600 rpm then Why we had incresed speed in NPP & TPP???
I NEED RRB APTITUDE QUESTIONS AND MODEL PAPER,PLEASE SEND MY E-MAIL joo28_eee@yahoo.co.in
why power generate in 33 kv it will be step down by 11 kv .
why dose not transformer not rotate ?