How the value of KVAR of capacitor bank used in switchgears calculated??
Answers were Sorted based on User's Feedback
Answer / abdul
It depends on the how much the power factor has to be improved
simple calculation would be
Kvar = KW [tan (cos inverse (old pf) - tan (cos inverse (new required pf)
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / girish
KVAR=KWX0.541(Power factor improvement at 0.98)
KW=20
KVAR=20X0.541
10KVAR
2.5KVAR 4 Steps
| Is This Answer Correct ? | 0 Yes | 1 No |
why electron not flow in open loop,how they know path is open ?
In response to Mr Bikas. If fault current is 52 kA then what will be the CT specification
What is a copper loss or i2r loss pc?
what is meant by CT`s saturation ? Can we use Metering CT`s with Protetection CT`s ?
what is the importance of fault level in power system and how is it decided
how technical is calculated in 11kv line and lt line
Who we calculate the generator NGR resistant, generator voltage 11 KV ?
what is the circulate the diesel in DG in side pls tell parts name and picture with circulate the diesel
cable tray sizing & selection
What are the loading factors to be considered for transformer sizing/selection?
one cable insulation resistance 200 mega ohm. how find 250 meter cable resistance.
Between rotating armature type and rotating field type arrangements which one is adopted for large rated alternators and DC generators.Why there is difference in the choice?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)