How the value of KVAR of capacitor bank used in switchgears calculated??
Answers were Sorted based on User's Feedback
Answer / abdul
It depends on the how much the power factor has to be improved
simple calculation would be
Kvar = KW [tan (cos inverse (old pf) - tan (cos inverse (new required pf)
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / girish
KVAR=KWX0.541(Power factor improvement at 0.98)
KW=20
KVAR=20X0.541
10KVAR
2.5KVAR 4 Steps
Is This Answer Correct ? | 0 Yes | 1 No |