does the power factor of an induction motor improve upon
used in parallel with a synchronous condenser , used
commonly to provide a leading kva ?
Answer Posted / rakesh
when a synchronous condenser is used in parallel with an
induction motor ( which normally operates at a low pf at
light loads) then the power supply to which an induction
motor is deriving its power from is relieved of providing
reactive power to im , while the im still draws the same
reactive power as before , the necessary kva is now
provided by the condenser as it exports reactive power.
hence the pf of im remains the same but the pf of the
combined system of im and sc is improved .
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
how to select energy meter? have any calculation?
In radial network the source is fed from 1 end both ends at central
The 3 phase 400 hp 440 volt slip ring induction motor do not take one phase amps why ? The motor is running good condition
If there is major % of Voltage harmonics in the system, how can it be control or reduced?
If a high resistance fault occurs,then what are the changes will happen in the system?
Differentiate between voltage and current feedback in amplifiers?
Classify milling machines.
limitation of conductor height on ground when we consider EMC
How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?
Define rise time.
Can we use shunt trip coil instead of trip coil with protection relay for protection?
what is earthing.how we make it,describe briefly.
Draw torque - speed curve and load curve of induction motor? mark operating point ?
how we can set the IDMT relay.
what is the difference between Central Battery System and UPS in applications and uses? and why UPS suitable for Computers and central battery for emergency lighting?