Answer / p. sudhagar
Megger is used to checking in insulation value,Its used to
high voltage injunction purpose and checking the polarity.
Contact resistance meter used to checked the contact
resistance value, Its injected the 100A only So its
resistance value low.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sanjeev
megger is a insulation Resistance checking with applied voltage for checking purpose but contact resistance meter only measuring in oms
| Is This Answer Correct ? | 5 Yes | 3 No |
how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?
how can we calculate cable size
What is the difference between RMS and average value
List some examples of renewable energy?
What happen if we re-start H.T motor whose rotor is running at 40% rated speed. Is it will damage motor winding?
11KV AND 22KV NETWORK KW CAPACITY IN RING AND RADIAL?
What is the accepted limit to increase the choosen transformer capacity over the load and why ?
why do we use star-delta starter. what is its need?
Briefing the effects of ASR and ACR of a double closed-loop speed regulating system.
What is the percentage loss for aluminium wire for HT line more than 11KVa
single sphase energy meter measur
What will happen if I apply DC to AC transformer? please send detailed answer at habib_rahman_habib786@yahoo.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)