how to calculate short ckt current of trafo.
ex.3-ph 3MVA trfo. 11/440, impdence voltage=7.25%
Answer / annonymous
Fault MVA = 3MVA/0.0725= 41.38MVA
So fault current on 11kV side= 41.38/(1.732x11x0.8)= 2.715kA
fault current on 0.440kV side=41.38/(1.732x.44x0.8)= 67.87kA
| Is This Answer Correct ? | 1 Yes | 0 No |
I have 1500KVA transformer ,How much Maximum KW Load is allowed?
15 Answers GKC Projects Limited GKCPL,
what is T P N bus bar
How to make vector group test of transformer?
How we can make sure cable size of LT cable without any parameter.
2 Answers Paradip Port, Siemens,
what can be the causes of capacitor start motor having a higher current that its actual
what is the earth resistance ?
what is the differnce between ac and dc?
why 6.6,11,22,33,66kv? what basis they have considered?
What is the effect of interchanging core(made of steel) and winding(made of copper) material in case of transformer? Give proper explanation in regard to different losses in transformer.
In a Impedance Based Distance Relay (Quad Characteristics) - Could there be two different Line Angle(RCA) for Ph-Ph & Ph-Gnd? If So Kindly Let me Know.. Where, What are the advantages of the same?
What is critical disruptive voltage?
why aggregate is placed all around substation ground.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)