how to calculate short ckt current of trafo.
ex.3-ph 3MVA trfo. 11/440, impdence voltage=7.25%
Answer / annonymous
Fault MVA = 3MVA/0.0725= 41.38MVA
So fault current on 11kV side= 41.38/(1.732x11x0.8)= 2.715kA
fault current on 0.440kV side=41.38/(1.732x.44x0.8)= 67.87kA
| Is This Answer Correct ? | 1 Yes | 0 No |
Which type of a.c motor is used in the fan (ceiling fan, exhaust fan, pedestal fan, bracket fan etc) which are find in the houses ?
How we select the vector group of 3phase power transformer?
Pls explain about full theory of salient pole generator?
What do you mean by screen of power cables?
why do we prefer a 3-phase delta connected load rather than star connected?
In a 3 phase induction motor(without connecting supply) if we rotate its rotor by hand and check resistance of stator winding at motor terminal box its resistance varies why ??
deisel generators all elcetical calculation formule's
Did RMU have ct and pt ?
in an industrical wiring, why we are using lighting DB and Power DB separately?
how to deside the capacity of chock for drive?
What is the inside of ACB & VCB & SF6 breaker's pls tell me about this
In liquid rotor starter how PH valve should be maintained.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)