Why should we use Star-Delta connection in step down power
transformers?
Answers were Sorted based on User's Feedback
Answer / harishchandra
in Y the vL=1.73*vp
in delta vl=vp and current IL=1.73*ip
also for distribution required 230 n 433v so neutral is
required so we used y - delta conec.
| Is This Answer Correct ? | 23 Yes | 7 No |
Answer / hussain
Actually we use Delta-Star connection for step down to get
neutral in the secondary. The question is wrong , should
read why we use delta-Start connection , not opposite.
| Is This Answer Correct ? | 18 Yes | 7 No |
Answer / guest
1:--- actually we used delta -star connection in power
distribution transformer to provide the returning path of
current,because connected load does not balanced so
returning current goes to transformer star point through
neutral wire which always earthed.
2;---In distribution load is being different type like
single phase three phase etc so we have required neutral for
single
phase load which is only possible in star connection.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pkv
actually delta star trnasformer used in step down
trnasformer to avoid earthfault give effect of over
current on hv side of the trnaformer
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / arindam
Delta is mainly used on low voltage side because its line voltage=phase voltage. if it is used on high voltage side due to high voltage in phase more insulation is required. But if it is star then its phase voltage = (1/√3)phase voltage. so if high voltage applied to line of star its phase value decrease by √3 times and comparetively less insulation is required. Hence star-delta is used for step down and delta-star is used for step up.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / rafeek
question is wrong,
normally we use delta-star connection for step down
transformer to prevent earth faults.
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / paramesh
Because starting voltage of the star connection is less
compare 2 other connections..........
| Is This Answer Correct ? | 6 Yes | 17 No |
which protection are used for turbo generator in thermal power plant.
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
Use of electrical theorems (thevenin's,norton's,millmen's,superposition,reciprocity, Maximum Power Transfer theorem,Compensation Theorem) IN REAL LIFE???(IF YOU KNOW EXACT OR CORRECT ANSWER).
2 Answers College School Exams Tests, L&T, PESIT, Wipro,
please anybody help me to find out the BHEL trainee Exam previous year questions papers . if u ve pls. send it to surekhared@gmail.com
What will happen if we give transformer a dc not ac
Why is remote backup preferred to local backup?
Why does the speed regulating system adopting I controller have no steady-state error? In this single closed-loop speed regulating system, when the input of the I controller Un=0, what is the output voltage of the regulator? What factors do the output voltage depend on?
i have a roll dia aprox.43 inches and gear box ratio is 14.3.so my question is how was decide the kw rating of motor.
MCCB 400 Amps 50KA 430Volt AC What is mean by 50KA
how to calculate the ct burden?
What is the meaning of In,Io & Ir in Circuit breaker? How to calculate?
what will hapen if we give ac supply to dc motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)