If ur Load is balanced in three Phase supply system Neural
current is Zero . neutral current is always depend on the
Unbalance load. So in Case of 3 phase system neutral bus
taken half of Main bus.
but in case of 1 phase supply system neutral is the return
cunductor and phase current will be equal to neutral curent.
so In 1 phase neural would be of same size.
as In three phase, current in neutral in one third
of phases so conductor size is less. but in single phase neutral conductor size should be same as phase conductor size
| Is This Answer Correct ? | 6 Yes | 4 No |
I AM INTERESTED TO WIND A 3 PHASE MOTOR HOW I CALCULATE TURNS, PITCH,AND WIRE SIZE FROM STATOR DIMENTIONS
What is difference b/w fuse and breaker?
Is there any problem if i connect APFC panel in generator circuit
what is XLPE type cable
why connecting surge unit in contactor coil
Why did lightening arrestor solid copper rod head is sharp on mobile tower top?
what is the Maximum voltage range for single phase
Where there is voltage,there must be current.Is this right or wrong??
how i calculate the size in mm of the LT 4 core cable for 100 HP inductive motor pump
selection of conductor in different voltage?
why to use freewheeling diode ( diode in revers bias mode) across dc coil
what is the type of winding connection( star or delta) in 1HP to 5HP motors. How to check the motor winding connections( star or delta) if not provided in the nameplate?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)