We are having Chemical earthing pit
the voltage between neutral to earth showing 22V how to
solve that
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
There is a loose connection in the neutral conductor before
the point of testing. whenever there is a loose connection
in the neutral wire, the neutral point gets shifted to the
point of loose connection.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / vinod
the neutral earthing in transformer may not be perfect or
brek in neutral from transformer
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / tulshiram
Connection of your mesuring equipment to earthing strip is
not proper, First correct connection & then measure it, if
found again please shift your earthing pit postion or
fill/give more water for earthing then meassure.
| Is This Answer Correct ? | 0 Yes | 0 No |
Please tell me if you are electrical engineer,and you are appointed for the maintainance of Electrical Power plant,then which parts of the plant deal with you.Also tell how these parts/components work.
what is linear motor?
What's difference between a400amps lt contactor and a400amps lt circuit breaker
generally on the roadside v hav 11kv line which is being step down to 440v line to line....so any1 can tell me which type of transformer they r using whether it is star to delta,delta to star etc...???
at present how many EHVAC lines are there in India?
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?
What is meant by vector group
0 Answers GPSC Gujarat Public Service Commission, VA Tech Wabag,
Why iron core losses are constant at all loads in a transformer ?
what is the efficiency of thyristor
I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF
What is Skin effect of the cable?
What are differences between Conventional & Addressable type smoke detectors?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)