What is auto reclose system in Circuit breakers??
Answers were Sorted based on User's Feedback
Answer / nagendra
Whenever a fault occurs the circuit breaker trips.Reclosing of the breaker automatically when the fault on the system cleared is known as auto reclose system in circuit breakers
Is This Answer Correct ? | 20 Yes | 8 No |
Answer / raul
basically there r 3 types of faults..... transient fault
(80%), semi-permanent fault (12%) and permanent faults
(8%). transient fault occurs only for a small duration, the
CB is opened for a short duration of time so dat d cause of
failure is cleared and the line is re-closed by closing the
CB. for semi-permanent faults which r basically due to a
twig falling on d line or a bird spanning around a
conductor.......the auto-reclosing after the cause is burnt
away.........and finally the permanent faults ie single
phase permanent fault n 3phase permanent fault.....for 1-
phase fault, the remaining two phases r operational n the
faulted phases is taken out for repairs n after d repair is
done the line is reclosed n for the other 3-phase fault,
the complete 3-phases r taken off for repair n after d
repair is done, all d 3-phases r reclosed
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / vinod
Auto reclose is using in transmission line circuit breaker
with selection of single phase, three phase or single and
three phase.
In transmission line there is chance of momentery fault,
based on the area and lenth the time and times of auot
reclose being selected.
Is This Answer Correct ? | 1 Yes | 11 No |
Answer / tarun purohit
When any fault occures in line,the circuit breaker trips the supply off to the line.This is called the auto reclose system in Circuit breakers.
Is This Answer Correct ? | 4 Yes | 19 No |
What happens if there is no nuetral in the power system?
On which side, taps are provided in tap changing transformers and why?
how is the many rpm of acb charging motor ?
What was your role in the silicon evaluation/product ramp? What tools did you use?
when we decide to use soft starter drive or vfd drive in mcc to operate apump?
Our transformer capacity is 500kva & voltage ratio is 11kv/433v step down tf.Now i need to know if my input voltage is 10500v and what would be the secondary side voltage i.e output voltage ?
How to measure 20 hp motor resitance
What is Form factor?
What are the two segments of nyquist contour.
in 31.5 mva power transformer how to set of wti and oti?
what is meant by transformer oil temparature
hi guys please tell me the procedure for mesuring the coil resistance of 3ph induction motor?