why we commonly use delta star winding in power and
distribution transformers
Answers were Sorted based on User's Feedback
The best way to minimise 3rd harmonics in the transformers
there are two ways. Either transformermer has low flux
density which is not economical and not in use or to make
atleast one winding of the transformer in delta because 3rd
harmonics are absent in delta. Since the requirement of
three phase four wire system in distribution, we commonly
use delta star winding
| Is This Answer Correct ? | 25 Yes | 3 No |
Answer / gunasekaran
one voltage level single earthing is recommended that is at
source for G.T generator is source it is already earthed.if
we use star we have to do the earthing so delta connection
is preferred.for distribution sending end is already earthed
at substation so HV side of the distribution transformer is
delta for LV side transformer is source so star with earthed
neutral. if two earthing is provided zoro sequence current
getting closed path so wave farm become distracted.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / arvind sharswat
only most reson because i can gate 3phase and single phase with nutral in delta-star connection
| Is This Answer Correct ? | 1 Yes | 0 No |
Delta connection is make at primary side because in delta
low harmonics(3rd,5th and 7th) produce as compare to star
while at secondary side star connection is use to provide 3
phase 4 wire system or we can say that getting singale
phase from 3 phase.
| Is This Answer Correct ? | 15 Yes | 18 No |
Answer / a,karthika
because we can make earthing only in star connection.if
there is an excess amount of power which can be easily
removed by earthing.Hense secondary winding is a srat
winding
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vinod meshram
in my thinking we use for getting nutral only because in
delta it is never possible to get neutral.We get neutral on
secondary side for distribution perpose.
| Is This Answer Correct ? | 2 Yes | 8 No |
Answer / e venkat reddy
In Delta connection it requires only three wires to
transfer on power but in star it requires 4 wires to
transfer the same amount on power so we are using delta at
primary side.because availability of neutral we are using
star connection at secondary side. In delta side the zero
sequence is current also zero.
| Is This Answer Correct ? | 7 Yes | 14 No |
You are given 220 V supply source, four wires, an ammeter and voltmeter. There is no any indication or description on meters. How will you identify which is ammeter or voltmeter?
why normally Generator rating are between 11Kv to 22Kv?
the distance from my office to d.g is aprox 400mtrs and voltage drops ibn my office near about 40 volt what should i do p[ls suggest.
bitumar
160 kw motor running use 2R* 150 SQ mm cable
can we install HT panel & LT panel side by side or how much clearance is required ?
How can we choose the rating of submersible motors
when the supply of MSEB is cut off & all the load of the industry is driven on generator at that time the capacitor which is connected in industry for power factor control is switched off why?
Does the ferranti effect has some impact on the electricity billing system on high voltage installations?
what you have to see after one week or month from the day of installation of transformer ?
How to calculate the NGR value for a 2.7MVA Transfomer, 11KV system where the fault current has to be limited to 50A?
In case you don't have coal and salt for earthing, how can you achieve good temporary earthing?
1 Answers Focus Energy, NHPC, ONGC,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)