why we commonly use delta star winding in power and
distribution transformers
Answers were Sorted based on User's Feedback
The best way to minimise 3rd harmonics in the transformers
there are two ways. Either transformermer has low flux
density which is not economical and not in use or to make
atleast one winding of the transformer in delta because 3rd
harmonics are absent in delta. Since the requirement of
three phase four wire system in distribution, we commonly
use delta star winding
Is This Answer Correct ? | 25 Yes | 3 No |
Answer / gunasekaran
one voltage level single earthing is recommended that is at
source for G.T generator is source it is already earthed.if
we use star we have to do the earthing so delta connection
is preferred.for distribution sending end is already earthed
at substation so HV side of the distribution transformer is
delta for LV side transformer is source so star with earthed
neutral. if two earthing is provided zoro sequence current
getting closed path so wave farm become distracted.
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / arvind sharswat
only most reson because i can gate 3phase and single phase with nutral in delta-star connection
Is This Answer Correct ? | 1 Yes | 0 No |
Delta connection is make at primary side because in delta
low harmonics(3rd,5th and 7th) produce as compare to star
while at secondary side star connection is use to provide 3
phase 4 wire system or we can say that getting singale
phase from 3 phase.
Is This Answer Correct ? | 15 Yes | 18 No |
Answer / a,karthika
because we can make earthing only in star connection.if
there is an excess amount of power which can be easily
removed by earthing.Hense secondary winding is a srat
winding
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vinod meshram
in my thinking we use for getting nutral only because in
delta it is never possible to get neutral.We get neutral on
secondary side for distribution perpose.
Is This Answer Correct ? | 2 Yes | 8 No |
Answer / e venkat reddy
In Delta connection it requires only three wires to
transfer on power but in star it requires 4 wires to
transfer the same amount on power so we are using delta at
primary side.because availability of neutral we are using
star connection at secondary side. In delta side the zero
sequence is current also zero.
Is This Answer Correct ? | 7 Yes | 14 No |
what happen if i connect DYn11 and DYn1 vector group transformer in parrallel?other things are same like votage ration,x/r ratiob etc...
Why we say three phase voltage 440v.
For 280kw power. Which cable I can usr
what is MUSS?
In a three-phase full converter, every SCR conducts for a.60deg. b. 120deg. C.180deg. d.90deg
How to justify this statement ??? "Capacitors in series provide less capacitance but higher voltage breakdown rating for the combination"
What is thef ormula to calculate the rating of a capacitor for a single phase motor
how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?
0 Answers Bhel, Jai Balaji, Rashmi Group,
What should be ideal IR value for 11kV, un earthed, 1 MW motor?
1.why are not using acb 33kv ht side? is there any problem 2.what is difference between acb,vcb,sf6 breackers? 3.what is the function of invertor and convertor in ups?
how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula
Can we Co-ordinate relay in Load Break switch?